I have a mirror cabinet with lighting and a built in shaver socket.
The retailer sent an electrician over to check if it was earthed, as apparently, some were not.
He also checked to see if the shaver socket had an isolating transformer fitted.
The electrician checked the earth by looking to see if a CPC was connected (it was).
He checked the shaver socket to see if it had an IT fitted (it did not).
He also checked the position of the cabinet to make sure it was outside the zones (it was).
He declared it safe as apparently the socket outlet only needs an IT if it is in Z1. He also declared it safe as there was a CPC connected.
Regs say except for SELV sockets and shaver supply units complying with 61558-2-5, no socket outlets should be installed within 3m of the boundary of Z1.
The retailer sent an electrician over to check if it was earthed, as apparently, some were not.
He also checked to see if the shaver socket had an isolating transformer fitted.
The electrician checked the earth by looking to see if a CPC was connected (it was).
He checked the shaver socket to see if it had an IT fitted (it did not).
He also checked the position of the cabinet to make sure it was outside the zones (it was).
He declared it safe as apparently the socket outlet only needs an IT if it is in Z1. He also declared it safe as there was a CPC connected.
Regs say except for SELV sockets and shaver supply units complying with 61558-2-5, no socket outlets should be installed within 3m of the boundary of Z1.