H
holmslaw
..
What do you do about 523.8 and 433.4.2?I don't think a 20A RFC is recognised by the regs?
Yes it is, as is any other properly designed circuit.
It isn't the examples I was thinking of, it is the specific regulation regarding ring final circuits which includes protective devices, cable sizes etc.I don't think a 20A RFC is recognised by the regs?
Yes it is, as is any other properly designed circuit.
The examples of ring and radial power circuits are options, i.e. there are other ways of skinning the cat.
No, but other designs would not comply with 433.1.5.The specific regulation you mention [433.1.5] does not preclude other designs.
What about final circuits for socket outlets, i.e. the type under discussion - what do you do about 523.8 and 433.4.2?'Industrial power rings' with an protective device of 200A or 100A were quite common - these would now be classed as distribution circuits, but the principle still applies. They are a poor mans alternative to bus-bar trunking - IMO not very nice - but they can be made compliant with BS 7671.
Some used overhead line taps as connection units. These can have an insulated cover placed over them but it sometimes drops off if disturbed - with electrifying results .
No, but it's the only one which explicitly permits ring finals where the OPD is higher rated than the cable.433.1.5 only considers ring final circuits protected by 30A or 32A devices, wired using conductors with a minimum CSA of 2.5mm². As such it does not apply to other designs.
Indeed, but the whole point of a ring final is that the OPD has a higher rating than the cable, so I assumed that in any alternative RF design you'd still want that.A design using a 20A protective device might be wired using 2.5mm² and, subject to installation conditions, this could comply with BS 7671 generally, including 433.4.2.
No, it does not, but the only regulation which supports ring finals is 433.1.5.523.8 does not preclude ring final circuits and the definition of these is not specific to cable or protective device sizes.
This discussion is about ring final socket outlet circuits.Now all you need to do is differentiate between a parallel circuit and a ring circuit, or prove that they are one in the same, and you might have a case against an industrial power ring .
Indeed, but the whole point of a ring final is that the OPD has a higher rating than the cable, so I assumed that in any alternative RF design you'd still want that.
433.4.2 would not let you use a 20A OPD if the cable was not rated at 20A.
This discussion is about ring final socket outlet circuits.
This is great - the Titans of the forum clash
Who is winning?
That's true.Why is it the "whole point"? There are other consideration such as the number of load points that are traditionally connected; voltage drop; functional earthing to name a few.
But it's always the case in domestic socket outlet ring finals, and it's always a main advantage, as things like volt drop are unlikely to be an issue.The fact that a reduced cable size can be used under certain circumstances is useful, but it is not the only justification.
Read the OP again BAS it is not that specific.
Hi guys, could someone gave me, or direct me to, a general overview of how a house is wired.
This is great - the Titans of the forum clash
Who is winning?
I think you know there can only be one winner, as the BAS-inator will not stop until all his enemies are dead, or at least completely belittled