Expansion vessel unvented cylinder

Joined
18 Mar 2018
Messages
1,205
Reaction score
80
Country
United Kingdom
If you go to a prv dripping and cold water expansion vessel has no charge. Do most people recharge? We have to depressorise and remove to do that. So it it easyier to just fit a new vessel ?
 
Nope - dead quick and easy to re-pressurise with the correct type of pump, though if it is a remote EV (not an in cylinder baffle type) then it should really be done at service time by a qualified Unvented chap.
 
Thanks yes I have my G3. Have a pump etc. is a remote vessel yes. It needs removing ideally to repressure it
 
It needs removing ideally to repressure it
As long as you can get the connector from the pump to the top of it then it should be able to be done in situ, I have a stirrup type pump that has a 3m hose on it for exactly that kind of thing. if not then it's a drain down and remove.

Don't forget to balance out the pre-charge to the mains pressure and expansion etc.
 
A stainless steel UV cylinder with its pressure reducing valve set to 3.0bar (with a recommended precharge of 2.8bar) and a EV sized to 10% of the UV cylinder's capacity will have a final pressure of just over 4.0bar if fully heated from 5C to 65C, its expansion relief valve might be typically set to 6.0bar and its T&PRV set to 8.0bar, example, below, of final pressure.

1769363929389.png
 
Last edited:
As long as you can get the connector from the pump to the top of it then it should be able to be done in situ, I have a stirrup type pump that has a 3m hose on it for exactly that kind of thing. if not then it's a drain down and remove.

Don't forget to balance out the pre-charge to the mains pressure and expansion etc.
Do you mean if the mains pressure is actually lower then 3 bar you'd charge to around 2 bar instead of 3?
 
Do you mean if the mains pressure is actually lower then 3 bar you'd charge to around 2 bar instead of 3?
Can't obviously speak for @Madrab but IMO the EV diaphragm should never bottom out, this is why a precharge pressure 0.2bar less than the PRV (pressure reducing valve) set pressure, usually, 3.0bar, is recommended, some say it also helps to prevent water hammer as the EV acts like a spring to even out any pressure fluctuations. The dynamic pressure might well drop to ~ 2.0bar at very high flow rates especially during periods of high usage, at certain times of the day. If you set the precharge to 2.0bar and leave the PRV at 3.0bar, then the "worst case" scenario is that say during the night while reheating the cylinder when the PRV pressure might well be 3.0bar is that the final pressure after a full cylinder reheat will be 4.58bar instead of the above 4.05bar. If you know that the static pressure will never be higher than 2.0bar and you set the precharge to 1.8bar and the PRV to 2.0bar then the final pressure after a full cylinder reheat will only be 2.81bar. Of course, in all cases, the cylinder pressure will fall to the pressure after the PRV once you run off the expansion volume, almost 5L, if a 250L UV cylinder is installed and pro rata for other UVC capacities.
 