Explain this fault then...

Joined
31 Mar 2006
Messages
20,030
Reaction score
1,396
Location
Leeds
Country
United Kingdom
We've not had a stinker on here for a little while, so who can work out what's going on here?



:twisted:
 
We've not had a stinker on here for a little while, so who can work out what's going on here?
Who can do anything but guess - but the first thing I'd probably do would be to have a careful look to see exactly what those two RCDs are connected to (and whether they are interconnected in some way!)!

Kind Regards, John.
 
Another wild guess: A ring final with an MCB on both ends; each on different RCDs?
 
Well the installation seems okay when power is supplied none of the MCB's have tripped - but the mechanical test on the RCD left causes an apparant earth fault to the RCD right.

Question did a mechanical test on the RCD right have the same effect to RCD left?
 