When working for GEC Large Steam Turbines we had separate crimp pliers for each size of crimp and they were calibrated and for 1mm we used different crimp pliers to 1.5mm even though the crimps were the same.
Orange 1mm and Red 1.5mm the same applied to 4mm and 6mm the crimps were same but pliers were different.
I got into a lot of trouble for using my own crimp pliers as they were not calibrated also for using my own meter as not calibrated. I was a different world where the motor and pump were lined up to within 0.001 inch. No allowing for layrub coupling taking up any out of true. But 5 years later on next shut down still had same coupling on all motors so seemed it did work.
Same in oil and gas (with the crimpers), not that anyone would ever have had the need to use their own intruments. New Fluke Exs and lop calibrators all round.
jkayes, ericmark talking of trouble with crimps has prompted me to ilustrate the trouble that can be caused by sparks (not electricians) or installers using cores for what they shouldn;t be used for and inappropriate crimping.
I also got told off for visiting a rig and asking around for the electrican asking him "are you the sparky"?
Why would any electrician call themselves a sparky, when that's a derogatory term?
The electrician I mean sparks who left the site because I was "impossible" (for going round and checking his work after him, insisting he dress cores in at JBs, use crimps at rotating machinery, not leave stray strands, test the crimp after fitting leave helices to alow burner and instrument retrieval, sequence terminal blocks, fit saddles at the same height) left a grand of damage plus time with his crimping and terminating skillz.
Before the winter break I saw him connect U1 V1 W1 together(instead of U2 V2 W2) on an extract fan motor (that's shorting all three phases together), I asked him WFTF that was and he said the motor has to be connected in Delta and pointed at the manual but he corrected it then asked about star delta starters (which aren;t appropriate for the installation). Two guys came to replace him so were advised they must check everything from the panel in that plant room before commissioning.
They obviously didn't - he hadn't crimped the crimps he had only placed on one Air Handling Unit motor. One crimp came off and the food hall supply fan motor burned out . He missed crimping the conductor on two of the phases on the extract motor on the same AHU with very nearly the same result, they pulled off in my hand. I cant be eveywhere and if they insist on sending sparks and not electricians the it's their own lookout if they introduce more problems
On the other kitchens air handling unit he couldn;t be bothered fitting a earth tag frying pan on the 4c SWA (armoured cable) into an ABS J/B for connection to the supply motor and had it in his head grey is always for earth when you don;t use the armour (because can't be bothered fitting the earth ring). So he used the spare neutral conductor for a phase although correct at the other end. Caught that one.
On the PWM controller for the kitchen extract he again used grey for a phase at the controller and for earth at the J/B and connected everythigng cotrrectly at the load side of the isolator but termnated the into PE (earth) in the controller. One expensive PWM controller down (though the M&E specifier forgot to add any means of speed control)
On a J/B for the de-stratification fans (stop the build up of hot air at ceiling height) he chopped a phase conductor, didn't tape it up but terminated the cable into 415V at the panel, giving me an almighty dunt. This is guy who thought himself a cut above the other electricians because he just paid for a Comp'Ex' and offshore survival. He wants to work offshore. That will involve doing electrical work on equipment in potentially explosive atmospheres. If he doesn;t cause an explosion (though equipment in gaseous areas is rated to handle such contained arcing) that will involve high value plant, electronics....