Extending Potterton 24 Flue

Discussion in 'Plumbing and Central Heating' started by Tom 31, 24 Nov 2021.

  1. Tom 31

    Tom 31

    Joined:
    23 Sep 2021
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom
    Evening everyone,

    We had some work done on the side of our house in the summer, a wooden lean-to style room that I'm using as a workout and storage space.

    We had someone round for some other work we want done and he needed to go into the new build area, he noticed that the boiler Flue is inside this new built room, I told the builder I wanted the Flue above the new roof, for obviois reasons, but when I got home he had put the new roof above the Flue so that it now sits inside the workout area.

    I'm not a builder and like most people take what builders tell you as gospel and he told me this would be fine as it's not a room used all the time and has more ventilation than a room inside a house. I noticed that when the boiler would run it would cause so much condensation on the steel roof that it was as if it was raining, so I ran some of the flexi pipe stuff you use for boilers from the Flue to outside, but the builder has told me how wrong this is and cut off my Gas till it can get sorted.

    Does anyone know if potterton allow you to out an extension on the Flue and take it out of the roof?

    This would save me dropping the roof altogether or moving the boiler.

    Sorry for the long story but the Mrs is on at me to ask online, the new builder is on this site as well I believe so he will confirm how shoddy the work has been.
     
  2. Sponsored Links
  3. kidgreen61

    kidgreen61

    Joined:
    8 Mar 2009
    Messages:
    2,491
    Thanks Received:
    602
    Location:
    Staffordshire
    Country:
    United Kingdom
    Is this a wind up?
    If not, turn the boiler off and get it sorted properly, you need a GS registered person to look and assess what you need.
     
  4. Tom 31

    Tom 31

    Joined:
    23 Sep 2021
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom

    I wish it was, I've got a GS person who is going to try and sort it, im just asking on here if the company that own potterton allow you to add an extension on the Flue, similar to a balcony extension or one with an elbow to go up and out of the ceiling ?
     
  5. Harry Bloomfield

    Harry Bloomfield

    Joined:
    30 Dec 2018
    Messages:
    9,554
    Thanks Received:
    1,293
    Country:
    United Kingdom
    Your builder needs shooting.
     
  6. Tom 31

    Tom 31

    Joined:
    23 Sep 2021
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom
    Not a million miles off what the guy said last night, lucky he came round when he did because we've only just started putting the heating on, been out there once with the boiler running and felt light headed and a bit woozy, thought it was because I was tired from nightshift
     
  7. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    13,431
    Thanks Received:
    3,104
    Location:
    Daventry
    Country:
    United Kingdom
    "Potterton 24" isn't super helpful I'm afraid - it just tells us it is a 24kW boiler made by Potterton. What's the model name please, or can you post a photo of the boiler?

    As above, your builder is very very wrong to tell you that it's fine to use in its present condition. It absolutely must not be used until the situation is rectified by a Gas Safe Registered Engineer
     
  8. Tom 31

    Tom 31

    Joined:
    23 Sep 2021
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom

    This is the boiler, it's a potterton performa 24, that's all it says
     

    Attached Files:

  9. polesapart

    polesapart

    Joined:
    27 May 2011
    Messages:
    1,386
    Thanks Received:
    362
    Country:
    United Kingdom
    Flue components for this (20 year old) non-condensing boiler will not be available.

    New boiler time, regrettably.

    Boiler relocation, reusing the salvaged existing flue unlikely to end well.

    "Builder wants shooting" -hell, yes.
     
  10. Sponsored Links
  11. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    13,431
    Thanks Received:
    3,104
    Location:
    Daventry
    Country:
    United Kingdom
    "Performa" was the missing bit of information.

    As Polesapart says, the flue is no longer available for this boiler, so your options are either change the roof, or get a new boiler. If you go for moving the roof, the finished surface of the roof must be a minimum of 300mm below the bottom of the flue terminal.
     
  12. Tom 31

    Tom 31

    Joined:
    23 Sep 2021
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom

    Cheers gents, not the news I wanted to hear, gutted I ended up with such a shody builder
     
  13. kidgreen61

    kidgreen61

    Joined:
    8 Mar 2009
    Messages:
    2,491
    Thanks Received:
    602
    Location:
    Staffordshire
    Country:
    United Kingdom
    You should report him to GasSafe, he could have killed someone.
     
  14. Madrab

    Madrab

    Joined:
    4 Oct 2012
    Messages:
    8,560
    Thanks Received:
    2,481
    Location:
    East Renfrewshire
    Country:
    United Kingdom
    That's a bit ironic after he built a room around the flue??

    I'd be going to town on this guy. Building Standards, EHO, Gas Safe ... I'd be calling them all and reporting him. As others have intimated, your boiler is what's classed as Immediately Dangerous and mustn't be used. The builder could have caused serious problems here to you and yours.

    Not to counter any of the pro's here but surprisingly it seems the flue and parts may still be available but you would need to contact them to confirm, some of these suppliers list them but don't actually have it.

    https://www.heatingspareparts.com/boiler-spares/partno/247719/240639
     
    • Like Like x 1
  15. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    13,431
    Thanks Received:
    3,104
    Location:
    Daventry
    Country:
    United Kingdom
    A RIDDOR report wouldn't go amiss either
     
    • Like Like x 1
  16. Gasguru

    Gasguru

    Joined:
    9 Sep 2005
    Messages:
    12,668
    Thanks Received:
    3,407
    Location:
    Sussex
    Country:
    United Kingdom
    You can report it direct to those that prosecute....

    Builders enclosing flues is a continual problem..

    https://www.hse.gov.uk/contact/concerns.htm

    I hope you're not relying on the builder to sort out the electrics/plumbing & heating...that's often a recipe for trouble (builders are well known for screwing over the other trades).
     
  17. gas112

    gas112

    Joined:
    27 Oct 2009
    Messages:
    23,035
    Thanks Received:
    8,236
    Country:
    United Kingdom
    Flue components are still available for these but are an extortionate price
     