• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

External appliances on RCD socket

Joined
6 Aug 2004
Messages
344
Reaction score
2
Country
United Kingdom
If the regulations say that in a domestic situation where you have sockets (in a house) where you will connect appliances for use outside, like a lawn mower, you have to have the sockets with an RCD; is it the same to put the sockets on a circuit that will be connected to the RCD side of the consumer unit or do you still have to have the RCD at the socket? and in this case not put the circuit on the RCD side of the CU?
 
You only need one (30mA) RCD in the circuit. If the circuit is fed from an RCD then there is no need to have an RCD type socket outlet. If the circuit feeding the socket is not RCD protected then an RCD socket can be used, though consideration must be given to other sockets on the same circuit.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top