It is rightPart of the N current from a load protected by a different RCD goes 'backwards' through the N side of the RCD protecting the circuit with a N-E fault, thereby creating an L/N imbalance (hence a trip, if enough imbalance) of that RCD ...
No. The full N current from load (as well as the full L current from the load) goes through the RCD protecting the circuit(s) with a load ("RCD1" in diagram above), hence no trip of that/those RCD(s)
Yes, I obviously misread your post. I thought you were saying both RCDs would trip.
This is the situation in Bernard's frequently posted diagram .