Ducted, double insulated Extractor Fan in loft switched with the light, timed over-run.
Been working fine for several years (note date lable 5/99) ... cleaned every year.
A 2 amp fuse required by manf in the fitting instructions, was not fitted by someone who knew better .. unfortunately he was a real sparky.
First pix shows plastic deformation of the outer plastic cover, on the corner at the shadow line.
Upon stripping the fan, this next pix shows the inner shell damage plus the burnt circuit board.
If you have an extractor fan in the loft, without the required fuse ... How do you fancy this going on out of sight ? Out of mind ? Out of home!!
Hope you can see why I have had a bee in my bonnet about it.
It's an awkward little problem to fuse both Live and switched live to the fan working in conjunction with the light.
P
Been working fine for several years (note date lable 5/99) ... cleaned every year.
A 2 amp fuse required by manf in the fitting instructions, was not fitted by someone who knew better .. unfortunately he was a real sparky.
First pix shows plastic deformation of the outer plastic cover, on the corner at the shadow line.
Upon stripping the fan, this next pix shows the inner shell damage plus the burnt circuit board.
If you have an extractor fan in the loft, without the required fuse ... How do you fancy this going on out of sight ? Out of mind ? Out of home!!
Hope you can see why I have had a bee in my bonnet about it.
It's an awkward little problem to fuse both Live and switched live to the fan working in conjunction with the light.