extractor fan installation
29 May 2006
I am considering installing an extractor fan in the bathroom.
The product I am thinking of is Manrose 100mm Bathroom Extractor Fan. The brief details are: (45dBA) Extract Rate 85m³/hr, 100mm Spigot, 15W Max 40ºC.
Our bathroom size: 3m x 1.5m x 3m and the bath is fitted with a thermostatic mixer shower.
If the extractor fan is suitable for our needs, does it need to be connected to the existing pull cord light switch and what is the correct cable size for the fan?
If you want it to come on whenever the light is turned on, and not come on if someone uses the shower without turning the light on, then yes.
The same size as the rest of the lighting circuit.
Don't forget to notify LABC if you live in England or Wales...
Also you will need to install an all - poles isolator switch, and depending on where in the bathroom you fit the fan, you may need to fit a SELV fand, rather than a mains one.
Please explain the alternative methods for the connection to get the fan working, for example when having a shower without turning on the light.
In addition, where do I find the address for LABC?
I like the idea of the isolator switch as suggested by RF Lighting.
The fan wall is at the far end of the bathroom, 3 meters away from the shower head and about 500mm away to the top right of the window.
What is a SELV fand? Please explain the circumstances when it is required.
A SELV fan is a fan which runs on an extra low voltage (i.e. 12v) supplied from a safety isolating transformer, if the fan was to be installed within the shower cubicle then a SELV fan will almost certainly be required; for general bathroom zone requirements see: http://www.niceic.org.uk/downloads/NL139supp.pdf
Some of the ways of installing the fan are to run it on its own leg from the lighting circuit providing its own switch, same way as if you were installing another light on its own switch. If the fan is not timed run on you may install it on a double pole pullcord and use this for both turning it on/off and isolation.
You may also install a separate isolator switch as RF says (note isolator needs to be in zone 3 or outside zones) and use a separate pullcord, this method is OK for timed run-on fans too.