What size and type of fuse protects the socket circuit?
So you have a 1.5 mm cable running off a socket that is protected by a 32 amp mcb?
I would recommend changing the cable for 2.5 mm, or protect the 1.5 with a 13 amp fused spur unit?
Out of interest, how many other cables are at this socket supplying the 1.5?
Why. As the circuit stands at the moment the cable is protected by the FCU at the load end. Does anyone read the regulations thoroughly ?
As I understood the post the cable FEEDING the boiler switched fused spur is fed in 1.5 mm. The 1.5 mm cable is spurred from a 30 amp ring circuit. So the 1.5 mm cable isn't properly protected in my opinion.
Advance appologies if I have misinterpreted the op.