What size and type of fuse protects the socket circuit?
So you have a 1.5 mm cable running off a socket that is protected by a 32 amp mcb?
I would recommend changing the cable for 2.5 mm, or protect the 1.5 with a 13 amp fused spur unit?
Out of interest, how many other cables are at this socket supplying the 1.5?
I would recommend changing the cable for 2.5 mm, or protect the 1.5 with a 13 amp fused spur unit?
I would recommend changing the cable for 2.5 mm, or protect the 1.5 with a 13 amp fused spur unit?
Why. As the circuit stands at the moment the cable is protected by the FCU at the load end. Does anyone read the regulations thoroughly ?
I would recommend changing the cable for 2.5 mm, or protect the 1.5 with a 13 amp fused spur unit?
Why. As the circuit stands at the moment the cable is protected by the FCU at the load end. Does anyone read the regulations thoroughly ?
As I understood the post the cable FEEDING the boiler switched fused spur is fed in 1.5 mm. The 1.5 mm cable is spurred from a 30 amp ring circuit. So the 1.5 mm cable isn't properly protected in my opinion.
Advance appologies if I have misinterpreted the op.