    in the instructions on our Grant Euroflame outdoor kerosene oil boiler it says that a pipe state fitted to the return water pipe may be fitted to offer frost protection and that it shall be set at 30 degrees centigrade.

    If water freezes at 0c i wonder why they say to set the stat at 30c ? - and wouldnt that use more oil in the end?
     
  2. Sponsored Links
  3. polesapart

    polesapart

    Joined:
    27 May 2011
    Messages:
    1,325
    Thanks Received:
    337
    Country:
    United Kingdom
    More likely the frost stat is integral (wouldn't you fit one as standard in a water filled expensive thing that lives outdoors) ; the pipestat is to reduce the amount the boiler fires after being triggered by the protective frost stat.
     
  4. leakydave

    leakydave

    Joined:
    2 Nov 2005
    Messages:
    959
    Thanks Received:
    102
    Location:
    Gloucestershire
    Country:
    United Kingdom
    Your boiler has a frost stat which fires the burner if the temp inside the boiler casing gets below about 5°C. To stop if firing for long periods, a low-limit stat can be fitted to the return pipework in the boiler, so that when the return temp reaches 30°C it will turn the burner off.
     
    • Thanks Thanks x 1
  5. oilboffin

    oilboffin

    Joined:
    26 Apr 2011
    Messages:
    1,665
    Thanks Received:
    247
    Location:
    isle of Lewis
    Country:
    United Kingdom
    You'll be in a world of pain if you don't have a frost stat.Bob
     
  6. andyr123

    andyr123

    Joined:
    17 Oct 2005
    Messages:
    112
    Thanks Received:
    0
    Country:
    Ireland
    Thanks very much all - re wiring of the pipe stat is Diagram 1 right or Diagram 2 correct thanks?


    STAT1.jpg


    STAT2.jpg

    [​IMG] [​IMG]
     
  7. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,736
    Thanks Received:
    1,086
    Country:
    United Kingdom
    2
     
    • Thanks Thanks x 1
  8. Wildcat1961

    Wildcat1961

    Joined:
    19 May 2010
    Messages:
    345
    Thanks Received:
    71
    Location:
    Essex
    Country:
    United Kingdom
    With diagram 1 frost stat has no function.
     
    • Like Like x 1
  9. oilboffin

    oilboffin

    Joined:
    26 Apr 2011
    Messages:
    1,665
    Thanks Received:
    247
    Location:
    isle of Lewis
    Country:
    United Kingdom
    This may seem a daft question but on all the external grant boilers I've fitted a frost stat has always been fitted and I've been asked by grants a time or two to replace the frost stat under warranty when they've played up,and if factory fitted you'd think it would be fitted in a way so as to be economical would you not.Bob
     
  10. Sponsored Links
  11. andyr123

    andyr123

    Joined:
    17 Oct 2005
    Messages:
    112
    Thanks Received:
    0
    Country:
    Ireland
    i hear/read 2 different settings for the frost stat some sites say 5c .. then some say 0c - i have just set ours at 3-4c - on some grant condenser boilers (could be vortex) they have a non adjustable frostat set at 5c at the factory.

    If you had a pipe stat wired up as in diagram 1 at 30c I shoud think you could do away with a frost-stat altogether couldnt you because it will always be keeping the return water at 30c ? (and consequently the inside of the boiler outdoor module above freezing)
     
  12. oilhead

    oilhead

    Joined:
    29 Nov 2009
    Messages:
    2,093
    Thanks Received:
    503
    Location:
    Shropshire
    Country:
    United Kingdom
    Only for as long as the heating is timed. The frost stat overrides all timer setting.
     
    • Thanks Thanks x 1
  13. Wildcat1961

    Wildcat1961

    Joined:
    19 May 2010
    Messages:
    345
    Thanks Received:
    71
    Location:
    Essex
    Country:
    United Kingdom
    Burner would run whenever return temperature reached 30c or lower (fuel wastage).
     
    • Like Like x 1
  14. andyr123

    andyr123

    Joined:
    17 Oct 2005
    Messages:
    112
    Thanks Received:
    0
    Country:
    Ireland
    ah right , because its on the permanent live? - so if you wired the pipe stat at 30c on the permanent live and not the switched live then that would work ... but as wildcat pointed out - fuel wastage
     
  15. oilboffin

    oilboffin

    Joined:
    26 Apr 2011
    Messages:
    1,665
    Thanks Received:
    247
    Location:
    isle of Lewis
    Country:
    United Kingdom
    The boiler will only run for a very short while.Bob
     
  16. Wildcat1961

    Wildcat1961

    Joined:
    19 May 2010
    Messages:
    345
    Thanks Received:
    71
    Location:
    Essex
    Country:
    United Kingdom
    Back end rot can destroy a heat exchanger within a short space of time (SE)
     
  17. oilhead

    oilhead

    Joined:
    29 Nov 2009
    Messages:
    2,093
    Thanks Received:
    503
    Location:
    Shropshire
    Country:
    United Kingdom
    Just wire a frost stat independent of your timer, set a 5o in parallel with a pipestat on the return at 30o or so. Your boiler frost stat is already installed for the former, just limit with a pipe stat on the return. You know it makes sense.
     