With the best will in the world no-one can guarantee an external pipe will not freeze. Even if condensate is connected into a pipe internally that pipe can freeze after it exits the building if exposed to the elements.
Installers have taken all reasonable precautions to prevent frozen condensate drains, but whilst we have 110mm soil pipes freezing up then without either keeping the entire run to the point where it goes underground protected from frost then its difficult to do much more.
Some installers have taken no precautions whatsoever. I've seen several installations where the condensate drains running from Worcester boilers are several metres of uninsulated 21.5mm pipe running externally with almost no slope - Never had a chance once the temperature outside went sub zero.
The Worcester installation instructions clearly state that all external pipework should be insulated or a minimum of 32mm - and that runs should be as short as possible.