sorry if i didn t explaine propely gentelmen,it was 1.28 r1 r2 and1.42 for the e.l.i on a lighting cucuit wired in 1.5 on a 6amp breaker.i was lead 2 believe anything over 1.00 was a problem?
If (R1 + R2) is 1.2 then that implies a circuit length of 42 metres, which is well within even the OSGs quite restrictive table of conventional circuits.
Given the Zs max for a 6A Type B MCB is 8.0, corrected to 6.4 Ohms, then at 1.42 you are well within the limits.