Hive installation broke my PCB on boiler

Joined
14 Jan 2026
Messages
1
Reaction score
0
Country
United Kingdom
The tradesman installed the hive controller last night but it blew the circuit board on my Vokera plus 29c boiler. The boiler powers up and makes a noise but the indicitor lights don't work and there is no hot water or heating.
The tradesman connected the live and neutral on the left two connectors on the Hive, looped the live to the third connector. On the fifth connector (3) he connected to CN5 right on the PCB.
What went wrong?
 

Attachments

  • IMG_20260113_230733.jpg
    IMG_20260113_230733.jpg
    105.5 KB · Views: 10
The stat connection in the boiler is extra low voltage/volt free. Putting 230v volts through it is wrong, as you have found out.
 