BS1362 specifies many tests but, yes, those are the currents used for the Temperature Rise Test, which is the one that people always cite if they want to argue that double sockets are 'rated' at 20A. They don't seem to understand that BS 1362 merely indicates a minimum requirement, and that there is absolutely nothing stopping someone manufacturing a BS 1362-compliant socket with a 'rating' of 26A if they so wish.
Yes I totally agree with you John.
"Point (in wiring). A termination of the fixed wiring intended for the connection of current-using equipment."
I see no conflict there I`m afraid - a twin socket has three terminals basic 9OK it might have an additional E terminal in some but not in others.
The way I see it a twin socket in a twin box yet two single sockets in a dual box (aka Bar Box) one is one point with a 13A total as per BS but the other is virtually the same in practical usage yet is two points and is 2 x 13A total as per BS.
If the particular manufacture at least complies with the ratings then I am sure that the proprietary manufacturers exceed them, often y a great amount and I would have faith in two x 13A simultaneous loads not being an actual problem.
the 13A rating is stamped on the back of the sockets for all to see, if we saw such a label etc on a cooker or hob etc we would understand that it is the full maximum loading of the complete unit and not just one ring of the hob or one oven or grill.
If I saw an electric shower of, for example, 10KW rating with 2 or 3 elements on board the unit I would not be if it had elements of 5KW and 3KW and 2KW accordingly (I am not suggesting the 5,3,2 ratings are in anyway typical by the way).
I don't see a conflict there.
I was told, "the Technical Datasheets are written by the Marketing Dept."
That would not surprise me much