As per the thread title. I’m looking to add an electric hoist to my loft and it’s rated at 500 watts. Can I take a feed from the lighting circuit to run this?

As per the thread title. I’m looking to add an electric hoist to my loft and it’s rated at 500 watts. Can I take a feed from the lighting circuit to run this?

Could maybe change to a type C if that happened, depending on Zs?It should be fine, but there is a slight risk on start up of the motor, it might trip the 6amp MCB. Try it and see, and if all OK, you could add a 13amp socket for the lift, to the lighting circuit - if the hoist is fitted with a plug.

Or 5A.It should be fine, but there is a slight risk on start up of the motor, it might trip the 6amp MCB.

If you feel that will be complied with, then not a problem.314.1 Every installation shall be divided into circuits, as necessary, to:
(i) avoid hazards and minimize inconvenience in the event of a fault
(ii) facilitate safe inspection, testing and maintenance (see also Section 537)
(iii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced by equipment in normal operation
(v) mitigate the effects of electromagnetic interferences (EMI)
(vi) prevent the indirect energizing of a circuit intended to be isolated.
Back in the day of incandescent bulbs (and the day when no-one denied that there were 'bulbs'Likely as with aerial amplifiers and bathroom extractors having the odd item on the lighting circuit is unlikely to cause a problem, but you have to decide if you feel it will comply. Your writing out the minor works certificate not me.
Come to think of it, we have 8 down-lights in our kitchen. We used to have 8 x 50w bulbs in them. In addition. We had another 20 x 10w bulbs in/on/under the cabinets. That’s 600w in total. They’ve all since been replaced with LED's now because I was fed up changing them - I used to buy them in bulk!Back in the day of incandescent bulbs (and the day when no-one denied that there were 'bulbs'), I'm sure it was not unusual to have 500 W worth of bulbs on a lighting circuit, with sometimes all of them 'on' simultaneously. Indeed, in my house I have one room which has a total of 18 candle bulbs (in multiple 'chandelier-like'fittings. Back in the day, that was 18 x 25 W - aka 450 W, for just one room!
Indeed. Slightly worse' than my room I described, then!Come to think of it, we have 8 down-lights in our kitchen. We used to have 8 x 50w bulbs in them. In addition. We had another 20 x 10w bulbs in/on/under the cabinets. That’s 600w in total.
Same here. Mine is a very large house with a good few multi-bulb/lamp fittings - which I think tots up to a total of around 80 lamps/bulbs. 'Back then', replacing dead one was a tedious weekly, if not daily, task and, like you, I used to buy large batches of them every 2-3 months. Now that everything is LED, I buy a handful every year or two!They’ve all since been replaced with LED's now because I was fed up changing them - I used to buy them in bulk!
As one would expect with the 80 or so I have here, I've had to replace just a few over the years (even though I always buy 'the cheapest I can find' these days!), but very few. As I wrote, I now only buy a small handful every year or two!I’ve never had to replace one LED yet.
I’ve never had to replace one LED yet.
I’ve never had to replace one LED yet.
You are really lucky. I have worked in many houses where the LEDs failed faster than a halogen would have failed. That said, they were probably cheap bulbs.