    Hello,

    I am trying to replace an old Honeywell T6360 main wired thermostat with a volt-free smart thermostat.

    I have an worcester bosch greenstar 30i boiler


    The current thermostat is wired up as shown in attached photos. From my measurements and bolier digram, I believe the wires I have now are "1-red-Live", "3-blue-switch live" and "Green-earth"

    upload_2021-9-16_21-4-36.png

    upload_2021-9-16_21-39-48.png

    My understanding is that the thermostat is currently set up so that it operates as simple main voltage switch (as shown in below schematic).

    upload_2021-9-16_21-46-40.png

    ...and so, in order to replace the current thermostat with the volt-free thermostat, I would have to creat or add a 240V connection to the neutral and live terminals (as shown schematic below), which would then power the new thermostat. I am planning to get this new 240V from fused termail which could be turned on and off with boiler.

    upload_2021-9-16_21-50-6.jpeg

    I will connect the old "1-red-live" and "3-blue-switch live" to volt-free terminal which are 3 and 4. Therefore the new circuit connection for using volt-free thermostat will be:

    upload_2021-9-16_22-6-9.png

    I did some search said the volt-free contacts could work with 240V. Am I right?

    I would be grateful for anyone's comments on any of the above, and/or any advice as to how best to go about this installation. Thanks
     
    Last edited by a moderator: 16 Sep 2021
  2. Sponsored Links
  3. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    8,529
    Thanks Received:
    2,236
    Location:
    North
    Country:
    United Kingdom
    Yes your understanding is correct, you do need to supply a permanent live and permanent neutral, then you can use either the volt free contacts or 5 & 6 which are common and normally open (a bit like how your Honeywell works now), and also suitable for mains voltage.

    Volt free means you apply the voltage to those contacts, usually 24v up to 240v.
     
    • Thanks Thanks x 1
  4. Summer2021

    Summer2021

    Joined:
    16 Sep 2021
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi Chris,

    Thanks for your kindly reply. There is one thing I can not undertsand. Why they didn't connect the Netural (connection 2) to the old thermostat? From my undertanding is they didn't use the "Anticipator" as the heating system is Combi boiler? But why the combi boiler doesn't need the Anticipator? Any idea? Thanks
     
  5. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    8,529
    Thanks Received:
    2,236
    Location:
    North
    Country:
    United Kingdom
    Yes, your understanding is correct, they didn’t connect the neutral for the anticipator, but it’s still recommended for a combi - but it just means there’ll be larger temperature swings when not used in any system.
     
  6. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    22,834
    Thanks Received:
    9,250
    Location:
    Lanarkshire
    Country:
    United Kingdom
    Because your existing thermostat does not have a heat anticipator, not all do
     
    • Thanks Thanks x 1
  7. DP

    DP

    Joined:
    10 Dec 2003
    Messages:
    14,627
    Thanks Received:
    3,200
    Location:
    Glasgow
    Country:
    United Kingdom
    Honeywell thermostat is volt free too :LOL::LOL::LOL:
     
  8. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    8,529
    Thanks Received:
    2,236
    Location:
    North
    Country:
    United Kingdom
    Do the older T6360’s not have them? This was from 2010 training manual
     