• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

IDEAL EVO HE - Bang on ignition

Joined
16 Feb 2010
Messages
2
Reaction score
0
Location
Sussex
Country
United Kingdom
Our Evo HE seems to suffer with this explosive ignition when it goes through the regular cycle of heating up the water inside so that when we draw water it's instantly hot.

I've noticed we have a dripping hot tap - could this drip cause the boiler to call for gas, but not enough flow to light the burner and then when the burner does light, we have a small explosion due to the excess gas???

Thanks.
 
It wont be the tap,its likely to be the ignition probe bent,or the spark generator.
 
Had exactly the same problem on my Ideal Evo, it was a bent earth strip connected to the spark generator.
 
Had exactly the same problem on my Ideal Evo, it was a bent earth strip connected to the spark generator.

I still have the problem. When the boiler bangs on ignition, I go up to the bathrooom and find a tap has not been turned off properly. Is it right that a dripping tap can start the ignition process so easily? So the boiler is trying to fire up, but there's not enough water flow to start it properly, then eventually the boiler does light and nearly comes off the wall!!!
 
Yep. very sensitive to dripping taps these boilers.
The sensor in the cold inlet registers on a slight change in temp and fires the boiler up
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top