Ideal ICOS HE15 question

All sorted ! many thanks to swbjackson for the PDF, it was clear as water :)


The primary control panel type dictates the jumper settings.

In my case

Primary Control panel with serial number ending 2 or greater : Jumper 2

Startup 0 followed by
2

Primary Control panel with serial number ending less then 2 : Jumper 1,2,3


Startup 0 followed by 1



Wow and I'm not even a fricking plumber, so what did I pay numbnuts to come out and do :confused:
 
Sponsored Links
Here's hoping Twofires is still around... or someone else with the PDF containing the jumper settings!

I've just moved into a property with a clicking Ideal Icos and I've narrowed it down to the display panel. There's a scribbled 'PCB' written on the user manual so I'm guessing that it (PCB, not the panel) was replaced at some stage... and possibly not had the jumpers set correctly.

Before I blindly follow Twofires' precis does anyone out there have a copy of the installation sheet giving the jumper settings for an HE15? There are a few 'serial like' numbers on the control panel so I don't want to start guessing which is the correct number to be referring to.

Regards,

Mathew
 