In the TN-C-S supply, which I assume is what I have in the UK...
By no means everyone in the UK has TN-C-S. Indeed, it was only a few decades ago that no-one in the UK had it. However, from what you describe, your supply is being used as TN-C-S - so, as I said, let's hope that the incoming distribution cable has been PMEd!
, the E only exists as long as the supply's N is intact.
Yep - although there may also be additional paths to earth via bonded metal supply pipes,like the ones that you imply you do not have (although many people do).
If incoming N gets disconnected, then the house has no E - EXCEPT random, undetermined paths, some of which could be someone taking a shower.
There should NOT be any 'undetermined paths to earth', and if there were then the installation would not be compliant with regulations - all possible extraneous paths to earth ("extraneous-conductive-parts") should be identified and bonded the the house's 'earth'.
Ironically, if your person in the shower somehow touched a live conductor, they would NOT receive a shock (and no current would flow through them) if nothing in the house was connected to earth!
I think the addition of one or more earthing rods would provide an extra layer of safety.
As I said,it will do no harm, but nor will it do a lot of good. As above, and as I said before, the most important thing is that all extraneous-c-ps are bonded to the house's 'earth', so that there can be no significant potential differences (which could cause electric shocks) between any two simultaneously-touchable metal things within the house.
What you you feel that an earth rod would protect you against, and how?