Are smoke alarms and extractor fans considered senstive equipment?
I very seriously doubt it - unless something has happened which reduced the insulation to (literally, or the equivalent of) a micron or two's thickness of PVC. Indeed, I actually suspect that voltages considerably below 250V would also not usually fail to pick up things which would be found at 500V[/quote]Does testing at 500V really demonstrate anything that won't be shown up at 250V ? I know that some faults don't show up at low voltage but we're not talking a few tens of volts, I'd be interested if anyone has ever found a fault that showed up at 500 but not at 250
If you're talking about L-N tests, then all loads need to be disconnected or else you'll just get silly (low) answers. If you're joining L+N and testing against earth, then it doesn't matter so much, but it's possible that L-E and/or N-E components or leaks within the load could muck things up.OK - Do I assume that standard practice is to leave them out or connect them up?
What do you mean by 'connected'? If you mean "connected and 'on'", and if you are talking about L-N tests, then, if the load does anything at all, then the measured 'IR' is usually going to be very low, making a nonsense of your IR measurement. However, again, if your talking L+N vs. E, then 'connected' is usually OK (but could occasionally give you a 'false' low reading, due to components/leaks in the load).My thinking was if they are not sensitive and connected up, then I would not only confirm IR for the circuit but also the equipment if reading >299Mohms.
Indeed, and this has come up before, in fact in a thread I started about doing some "quick" tests between tenants.However, again, if your talking L+N vs. E, then 'connected' is usually OK (but could occasionally give you a 'false' low reading, due to components/leaks in the load).
Indeed so, and I recall that discussion.Indeed, and this has come up before, in fact in a thread I started about doing some "quick" tests between tenants.However, again, if your talking L+N vs. E, then 'connected' is usually OK (but could occasionally give you a 'false' low reading, due to components/leaks in the load).
I'm inclined to agree, particularly in the context of a 'quick test'.From observation, in the flat I can do an IR test (L+N to E) at 250V fine with one polarity, but not the other - the RCBOs show a low reading one way but not the other. Thus I can leave everything one, open the main switch, and quickly test the IR - if it's reasonable then I see no reason to go any further ...
Indeed so - and, at least in the case of my MFT (Fluke 1652) one can't even overcome that by conducting two or more tests in quick succession - in the name of safety, the Fluke has a built-in 'auto-discharge' facility, and it won't let one doing a second test until the circuit has been 'discharged'!I can't do it with the MFT as the test isn't long enough to charge the caps in some equipment* which itself gives a false low reading - but Dad's old IR test set works fine as you can hold the button for a few seconds and watch the reading settle.