IR

no everything unplugged. the only thing i can think
is that i didnt take the fuses out of 2 fused spurs
 
Possibly though if this keeps happening at "lots of installations" (as per your original post) then you need to be a little more careful where you're putting 500v. You could end up with expensive repair bills.
I normally measure continuity between line and neutral and test at 250v before letting rip with 500v. Doing the two pre-tests 'should' highlight connected equipment.
 
i am careful about it. its just that the fused spurs were out
in the outhouse. everything else was out. there was def no other equipment connected
 
Well, bar a fault, the readings you obtained indicated something in circuit.
All I'm saying is be cautious before sending 500v down the circuit. A quick continuity test or 250v IR test would have highlighted the problem without even using 500v and risking damaging potentially sensitive equipment.
 
Hi,
I have found that if you leave the, say, neutral and earth connected to the earth and neutral bars and do not disconnect them that this sometimes can give you low readings, i.e. 50 - 70 Meg. If you disconnect the cables and IR test them individually, therefore treating them as a seperate lines and not taking all lines together then you normally find the resistance shoots up to plus 299 Meg. Could this be what yoru doing?
 
no i tested them seperately.
remembered today that the extractor hood was still connected.
is there a logical reason why the N-P reading was so much lower?
 
FFS.

You cannot do IR tests with any load connected.

You cannot do IR tests if the conductors are still connected at the consumer unit (hello...... Neutral and earth are closely connected, don't you know)

You shouldn't be testing if you do not understand these principles
 
DON'T STAND TOO CLOSE TO SECURE'S EARTH ROD!

Or is that a covert security method, jehovas witnesses at the door - flick the shower on :lol:
 