Is An Isolator In A Shower/bath Area Acceptable
I hate it as much as the next man, especially the cable that is clipped direct.
But, as RF says:
You can NOT put things on an EICR which comply with BS7671, just because you don't like them.
To be honest, the risks are probably lower than having an electric shower within the shower enclosure, and no body bats an eyelid at that....
As for moisture wicking up the cord, it may get so far, but it even if it manages to get to the top (which I doubt) it will fail to reach the switch mechanism because the cord joint will stop it.
You could legitimately note on the EICR any IP breach made by the surface entry cable.
EDIT. Sorry John, PBOD..... Another case of me not reading the whole thread... :oops:
Assuming the switch is over 2.25m above finished floor level to the bottom of the switch (excluding the pull cord), then it is permitted by BS7671.
You are completely correct RF but it is bad practice and as most showers are rated IPX4 it would seem that some accessories would have a higher rating and be subject to less water spray. I would also note that shower units should not have their casing altered to accept a cable entry which could compromise the warranty or IP rating as designated by the manufacturer. So in the eventuality of a shock they could claim not guilty. If at all possible I would always route the cable through the wall directly into the unit ensuring the seal works as intended.
Regarding putting comments on an EICR with things that do comply but could be improved. I would as far as possible put a comment in the summary or as an observation for advisory as improvement with no coding. At least it would cover me.
I will take a few more pics of before and after (if I remember) to show the situation more clearly. Thanks for your input.
I used to do a lot of PIRs and have on the odd occasion been pulled up on them and asked to justify my findings. I saw many things I didn't like and could have definately been done better, but the purpose of an EICR is to ascertain whether the installation complies with the current edition of BS7671.
I now quote the regulation number which is not complied with after every observation.
As for your installation, many showers allow top entry of both pipes and cables. Unless you can find a specific manufacturers instruction stating that this is not acceptable, then whilst not ideal, your installation is still compliant with BS7671.
I used to do a lot of PIRs and have on the odd occasion been pulled up on them and asked to justify my findings. I saw many things I didn't like and could have definately been done better, but the purpose of an EICR is to ascertain whether the installation complies with the current edition of BS7671. ... I now quote the regulation number which is not complied with after every observation.
Although that's true, as BAS has implied with his brief post, there are some regs which are very vague (134.1.1 probably being the most extreme example), hence allowing an electrician who is sufficiently confident that (s)he can justify his/her expert judgement/opinion to cite a regulation non-compliance for anything which, in their expert opinion, is 'unsatisfactory', even though there is no non-compliance with any 'explicit' regulation.
Kind Regards, John
I love 134.1.1.
It means that I can brand anything I consider shoddy to be a contravention of BS 7671.
I love 134.1.1. It means that I can brand anything I consider shoddy to be a contravention of BS 7671.
Provided, that is, that you are confident that you could justify your belief that not only was it 'shoddy' but also 'shoddy enough' to constitute non-compliance with the reg!
Kind Regards, John
If I consider it shoddy then my opinion, having exercised reasonable skill and care etc, is that it does not count as good workmanship.
QED.
If I consider it shoddy then my opinion, having exercised reasonable skill and care etc, is that it does not count as good workmanship. QED.
The 'QED' only really relates to that being your opinion. Others may not share you opinion (particularly if, for example, your opinion in question was that a lighting installation did not constitute 'good workmanship' because it consisted of downlighters :-) ).!
Kind Regards, John
134.1.1 is necessarily entirely down to the opinion of the person doing the inspection.
Hmmm - even if it were challenged? If you commissioned an EICR which resulted in a finding of non-compliance with 134.1.1 which, in your opinion, was unjustified, I reckon you'd probably be shouting about the 'lies and fraud' (or somesuch) that had been commited by the 'incompetent' person who had signed the declaration on the report!
Kind Regards, John
134.1.1 is great for use in theoretical discussions on Internet forums, but in the real world of EICRs carried out for paying customers it is far too open to interpretation and carries no real weight.
Frankly, I don't even think it's really much use in theoretical discussions on Internet forums, for the same reason - it doesn't stop the discussion being one about differences of opinion! However, I think you may underestimate how much 'weight' any 'finding of alleged non-compliance' on an EICR might carry in the minds of some paying customers. Given that it is so vague and subjective, I would hope that non-compliance with 134.1.1 is rarely cited on an EICR, but if people like BAS were doing them, who knows.
Kind Regards, John