    Having tidy up in shed today and took the time to have a look at the consumer unit in the shed.

    The feed from house to shed consists of TWO T&E running side by side in underground ducting. The conductors of both are joined together in a 60a switch box in the house and where they enter the consumer unit in the shed. One T&E looks like a 10a and the other a 4a. I assume the previous owner did this to up rate the supply as the shed was used as his woodworking workshop.

    Has this really up rated the supply and more importantly is it safe
     
  2. Sponsored Links
  3. RF Lighting

    RF Lighting

    Joined:
    31 Mar 2006
    Messages:
    19,990
    Thanks Received:
    1,354
    Location:
    Leeds
    Country:
    United Kingdom
    Not sure on your cable sizes there, but I suggest you have an electrician take a look.

    It might not be immediatly unsafe, but it is certainly an unconventional way of doing things.
     
  4. sealeon

    sealeon

    Joined:
    15 Sep 2008
    Messages:
    180
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    not sure on the two dfferent cable sizes but it is quite common to run two cables in parallel as a feed in some commercial and industrial installs.It would act as a ring final does but the two different size cables dont sound so good
     
  5. Stoday

    Stoday

    Joined:
    4 Oct 2004
    Messages:
    1,150
    Thanks Received:
    53
    Location:
    Suffolk
    Country:
    United Kingdom
    Using two different sized cables is frequent in distribution engineering, but not on installations in buildings.

    The reason is that in distribution the cable size is normally chosen for its volt drop, not on its current carrying capacity. Normally, the current carrying capacity is far greater than the limit set by the volt drop.

    On the other hand, in buildings, current carrying capacity is the driver and most cables are well withing the voltage drop limit.
     
  6. Lectrician

    Lectrician

    Joined:
    18 Jul 2004
    Messages:
    8,506
    Thanks Received:
    405
    Location:
    Devon
    Country:
    United Kingdom
    Two cables of the same CSA and the same length would be ok, although a single larger cable would be preffered.

    It isn't a 'ring final' it is simple two cables in parallel.
     
  7. holmslaw

    holmslaw

    Joined:
    12 Dec 2006
    Messages:
    5,841
    Thanks Received:
    400
    Country:
    United Kingdom
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  9. Sponsored Links
Loading...

Share This Page