At 240V, the current is 52A and the load is 12.5kW.
True - you did make that point before, and I'd forgotten that the 47.7A related to 220V. However, even if most people get about 240V, we're meant to do calculations at 230V, and (provided there are NO other loads) that just scrapes in for a 50A MCB at 49.9A !At 240V, the current is 52A and the load is 12.5kW.
We haven't discovered that.Are there any derating factors?
It does - which is why I said that it would probably be OK on a 50A MCB 'with most installations methods'.10mm² T+E has a maximum CCC, method C, of 63A.
Indeed...It is 5.5V @ 230V, 2.2%.
Mind you, if it is 10mm² cable, then 25m of that is going to introduce a VD of about 5.5V at ~50A.
Nothing. In fact, as I said, it 'helps' a little by reducing the current drawn by the kiln, making a 50A MCB a little more (just about) acceptable.What's wrong with that?
Ambient temperature will be significantly above normal at the garage end.Are there any derating factors?
Yes, probably (I haven't looked up the figures) but it clearly remains very marginal. As for the ambient temperature, even that 'outdoors' can rise into the 30s during a 'heatwave', and is commonly in the mid/high 20s, which wouldn't leave all that much scope for heating by the kiln.Then if the ambient temperature is no greater than 40°C (possibly 42 or 43) then the cable will be suitable.
I'm sure they aren't - but they get so hot inside, and tend to remain so for quite long periods, that I can but presume that they have an appreciable impact on temperature of the surroundings.I've never had a kiln but I don't think they are made to heat the room.
I wouldn't think so.Are they 'vented' to the outdoors in any way?
That was my guess. If that's the case, then all the generated heat has got to end up in the room (workshop/garage), at least until it escapes into the outside world. Think of five 2kW fan heaters running at full blast in the workshop/garage for a few hours!"I wouldn't think so.Are they 'vented' to the outdoors in any way?
Yes, that would solve that particular problem, if it existed (which I suspect it would).Anyway, some larger cable in the vicinity if necessary.