Kitchen Wiring Diagram
T
TomBridges
Hello everybody
We are planning on a new kitchen.. having drawn up an outline of what cupboards we are going to have, I have knocked together an outline of the electrics needed.
Basically I have a couple of questions:
1) Can all the appliances be put on the Ring Main? (As you can see from the diagram the Dishwasher, Washing Machine & Cooker Hood/Extractor Fan are protected by Fused Spurs.) I was wondering if I should have them on their own circuit? It seems like a lot of appliances/sockets for a 2.5mm 30amp circuit.
2) Does the cabling need to be shielded? or is it fine just under plaster?
Many Thanks in advance,
Tom
20 Aug 2009
Dorset
Generally it is ok to have a modern kitchen on one dedicated ring circuit, though some on this forum will bang on about having two or three radial circuits for the sockets.
It is good practice to use pvc capping or oval conduit to protect the cables during plastering. You don't have to have this protection, but it would be very sensible to do so. It's more professional. And makes future alterations easier. It won't cost much at all.
No need for those junction boxes supplying the fused spurs. Just run the two supply cables to the fused spur.
T
TomBridges
Hi sparkwright,
Thanks for your quick response.. I'm not sure what I was thinking with the jucting boxes actually.. though would be fun plastering them into the wall!
Tom
T
TomBridges
I did say in my post, and i quote "I'm not sure what I was thinking"..
5 May 2010
Stirlingshire
Washing machine only takes full current when heating the water, which isn't usually for very long. (Domestic) extractor fan is usually less than 100W.
Tumble dryers are a long heavy load.
You might want to put a separate circuit for the fridge/freezer on its own MCBO, so a fault anywhere else doesn't result in spoiled food.
Unless protected by steel conduit or specific cable types, all wiring now has to have RCD protection.
You might want under-cupboard lighting.
27 Aug 2003
London
"bang on", or point out the generic drawbacks with ring finals and the specific ones in a kitchen of balancing the loads when used for appliances, both of which should make the designer think about whether, when he's starting with a blank sheet of paper, a ring is the best design?
Proper plasterers will point out that the last thing they want to do is to damage the edges of their tools by hacking at cables with them.
The way to prepare for that is conduit rather than hoping you'll be able to pull new or extra cables through capping.
27 Aug 2003
London
Tom - you really do need to use an electrician. Apart from the legalities there are the genuine safety aspects of testing which you won't be able to do yourself.
You should consider having your old rewirable fuse box replaced at the same time, as the electrician is going to have to add RCD protection somehow anyway.
T
TomBridges
Hi all,
Thanks for your advice.
I am actually getting an electrician to do this work, though I am running the cables for 1st Fix electrics to save a bit of money.
So general consensus is a Ring Main is silly and I'd be better off with a 2.5mm Radial Circuit protected by a 30amp MCB?
Cheers,
Tom
5 May 2010
Stirlingshire
You need your electrician to specify the cable routes and cable types as he will be signing the work off.
You cannot have a 2.5mm radial circuit protected at 32A.
2.5mm is max 20A, and that doesn't give a lot of capacity for high current appliances. In fact in a kitchen I would suggest not having more than 1 double socket on a 2.5mm 20A radial, as you do not know how appliances will be distributed around the kitchen.
A properly specified and installed 32A ring final circuit should be sufficient for a domestic kitchen with the fixed cooking load on separate circuits. For a larger kitchen putting the fixed laundry appliances on separate radial(s) might be appropriate.
2 Jan 2009
Lanarkshire
That's a bit of a waste, using a 20A radial for a max load of 13A.
Colin C
