A "couple" of questions for the experts re my new kitchen wiring. I'm keen to get the wiring right as I'm going for the IEE Domestic Installer Scheme in the new year and want this to be one of the inspection installations. I do the 2381 training later this month but typically need to do the installation now. (As an aside: I fit bathrooms and the odd kitchen for a living but oddly no one locally seems to have heard of Part P!! Is this common - am I the only one spending upwards of £1k for this?)
Back to the point.... Current position is kitchen ring main feeding two double sockets and two FCU's. One FCU for freezer, the other for the cooker extractor. Under cupboard lights fed by feed from lighting circuit. One 32A MCB feeding the old cooker. Installation 12 years old, MEM split load CU.
Questions:
1. I want to install an additional dishwasher and fridge under counter top - can I supply these with an extention to the existing ring or even spurs from it? Or do I have to supply them via FCU's above the counter?
2. One wall structure is that horrible egg box construction meaning the ring extension will have to be surface mounted behing the cabinets. Is this permissable, assuming I keep to the vertical/horizontal rule from an accessory?
3. What's the best way to make the cable to cable connection for the ring extention of the ring ie within a socket box. Can I use crimps?
4. I understand supplementary bonding within a kitchen is not required under the regs but I always provide it, am I wasting my time and money?
5 New hob is rated at 6.3kW and cooker 2.07 kW. Current Cooker Connection is fed by approx 7m of 6mm cable under an uninsulated floor. My calculation says that this is 36Amps and the TLC volt drop calculator says that 6mm cable is ok? (The manufacturer suggests 4mm!). I'm very unlikely to use all 4 rings on the hob and the oven at the same time but can I trust these calcs?
Apologies the length of this and I appreciate your input very much.
Back to the point.... Current position is kitchen ring main feeding two double sockets and two FCU's. One FCU for freezer, the other for the cooker extractor. Under cupboard lights fed by feed from lighting circuit. One 32A MCB feeding the old cooker. Installation 12 years old, MEM split load CU.
Questions:
1. I want to install an additional dishwasher and fridge under counter top - can I supply these with an extention to the existing ring or even spurs from it? Or do I have to supply them via FCU's above the counter?
2. One wall structure is that horrible egg box construction meaning the ring extension will have to be surface mounted behing the cabinets. Is this permissable, assuming I keep to the vertical/horizontal rule from an accessory?
3. What's the best way to make the cable to cable connection for the ring extention of the ring ie within a socket box. Can I use crimps?
4. I understand supplementary bonding within a kitchen is not required under the regs but I always provide it, am I wasting my time and money?
5 New hob is rated at 6.3kW and cooker 2.07 kW. Current Cooker Connection is fed by approx 7m of 6mm cable under an uninsulated floor. My calculation says that this is 36Amps and the TLC volt drop calculator says that 6mm cable is ok? (The manufacturer suggests 4mm!). I'm very unlikely to use all 4 rings on the hob and the oven at the same time but can I trust these calcs?
Apologies the length of this and I appreciate your input very much.