Fitting new kitchen, replacing gas cooker with built in electric oven and induction hob both 13Amp and come with plugs fitted.
Existing Radial circuit 2.5mm 20Amp that runs above worktop.
wanting to have 2 sockets below worktop to accommodate the 2 appliances.
I assume I don't need to use 13amp fsu as appliances protected by 13amp plugs and seems logical I cannot spur of with a double for both appliances as the socket would be overloaded.
Is it better to run a spur then spur of again so I get 2 socket next to each other OR is it better just to run 1 spur from a socket then run a second spur farther up the radial on another socket.
thanks