Larger Capacity Gas Meter?

S

sturharv

Just some help please on what size gas meter is required.

The project is having various kitchen appliances equating to 135kW (there is some large 50kW oven and other baking appliances in there!)
Also there is a 50kW condensing boiler to heat the building. I understand that it is unlikely all the appliances will be running at the same time, but I assume the gas meter and supply pipe will have to be sized for that situation.

Therefore there will be a maximum load of 185kW.

What size gas meter would generally be sized for this. A standard domestic meter is the U6, what is the U16 capable of doing? or will it need to be larger than this?

I need to try and calculate the annual kWh's, has anyone got a 'rule of thumb' calculation for this?


:LOL: :LOL:
 
Sponsored Links
Joined
23 Feb 2007
Messages
21,178
Reaction score
1,936
Location
Norfolk
Country
United Kingdom
Most appliances will state what gas they will use at maximum in m3/hr.

Add all these figures up then see what meter will comfortably handle this ;)
 
Sponsored Links
Joined
24 Jul 2003
Messages
24,294
Reaction score
1,417
Location
London
Country
United Kingdom
A U6 = 6 cubic metres an hour will supply 60kW, or a bit over, but the "droop" in the meter can be significant.
So a U16 could cover it, but they'll only fit one for you for a mere few hundred quid if their supply to it is adequate, If not, they increase the size of their supply - at your expense, which is a lot.


OOps, I saw the 135, not the 185!
 
Joined
2 Mar 2007
Messages
3,441
Reaction score
69
Location
Lancashire
Country
United Kingdom
Somebody needs to get the Betnovate ready as an aris slapping is on its way :LOL: :LOL:

;)
 
Joined
8 Jan 2005
Messages
19,003
Reaction score
1,568
Location
Bath
Country
United Kingdom
A U6 = 6 cubic metres an hour will supply 60kW, or a bit over, but the "droop" in the meter can be significant.
So a U16 could cover it, but they'll only fit one for you for a mere few hundred quid if their supply to it is adequate, If not, they increase the size of their supply - at your expense, which is a lot.

Cough, Cough.

185 Kw = 17.29m³h

An U 16 is 16 m³h close but not quite close enough.
 
Joined
2 Mar 2007
Messages
3,441
Reaction score
69
Location
Lancashire
Country
United Kingdom
A U6 = 6 cubic metres an hour will supply 60kW, or a bit over, but the "droop" in the meter can be significant.
So a U16 could cover it, but they'll only fit one for you for a mere few hundred quid if their supply to it is adequate, If not, they increase the size of their supply - at your expense, which is a lot.

Cough, Cough.

185 Kw = 17.29m³h

An U 16 is 16 m³h close but not quite close enough

:LOL: :LOL: :LOL:

Somebody needs to get the Betnovate ready as an aris slapping is on its way

You was warned. now wheres that aris cream :LOL: :LOL:

;)
 
Joined
19 Feb 2006
Messages
30,830
Reaction score
9,954
Country
United Kingdom
Allowing for diversity factors a U16 might cut the mustard.
 
Joined
6 Sep 2007
Messages
335
Reaction score
7
Location
Essex
Country
United Kingdom
My fault didn't read the 185kw bit, just saw the 135kw.

Brain didnt register the rest. Seen similar though on u16 and seem ok, doesn't make it right though.

James
 
Joined
8 Jan 2005
Messages
19,003
Reaction score
1,568
Location
Bath
Country
United Kingdom
Diversity in a Commercial kitchen :eek:

Good practice would allow at least 10-15% higher than the calculated load.
 
Joined
2 Mar 2007
Messages
3,441
Reaction score
69
Location
Lancashire
Country
United Kingdom
For sure you get diversity in a com kitchen, I meet all nationalities on a daily basis DIA.

Oh and U25 is the way. on a domestic job now where we have had to upgrade to a U16, two boilers, large range cooker and two fires:cool: , Anyone got a meter tail for 15mm :LOL: :LOL: .

;)
 
Joined
26 Jun 2004
Messages
64,368
Reaction score
4,699
Location
London
Country
United Kingdom
Just some help please on what size gas meter is required.

Stuart, we know from your past postings ( which have not always been very polite to us who give you advice ) that you are apparently employed to design gas and heating systems.

Its very galling to a professional that you are able to do that work without having any qualifications or practical experience just because you dont touch actual gas fittings yourself.

Yet again my advice would be that you need to take sufficient training to be able to do your work without having to ask such basic advice on a free forum.

Alternatively employ a proper consultant to assist you.

Can I suggest that qualified people on this forum DONT give him this valuable free advice that he should really know himself or might at least pay for within the project costings.

Tony
 
S

sturharv

Ahh Tony, thought you may crawl out of your hole at some point!!

Again you seem better at slating the actual post rather than putting together a constructive or helpful answer to the actual question. I am not responsible for sizing the gas meters or other items which requires specialist knowledge (although for some reason you seem to know what exactly I do), I am simply curious as how these things work so I can understand what needs to be done i.e. costs for the work etc. so get off your high horse.

Tony, we know from your past 'postings' www.diynot.com/forums/viewtopic.php?p=816166#816166 that I am not the only one that you tend to annoy with your comments.

Keeping installing them combi’s Tony!!!!!
 