    Just some help please on what size gas meter is required.

    The project is having various kitchen appliances equating to 135kW (there is some large 50kW oven and other baking appliances in there!)
    Also there is a 50kW condensing boiler to heat the building. I understand that it is unlikely all the appliances will be running at the same time, but I assume the gas meter and supply pipe will have to be sized for that situation.

    Therefore there will be a maximum load of 185kW.

    What size gas meter would generally be sized for this. A standard domestic meter is the U6, what is the U16 capable of doing? or will it need to be larger than this?

    I need to try and calculate the annual kWh's, has anyone got a 'rule of thumb' calculation for this?


    :LOL: :LOL:
     
  2. Sponsored Links
  3. GforceJames

    GforceJames

    Joined:
    6 Sep 2007
    Messages:
    335
    Thanks Received:
    7
    Location:
    Essex
    Country:
    United Kingdom
    A U16 should be fine.

    James
     
  4. doitall

    doitall

    Joined:
    8 Jan 2005
    Messages:
    19,003
    Thanks Received:
    1,538
    Location:
    Bath
    Country:
    United Kingdom
    But then again perhaps it won't be.

    U25 mate. :rolleyes:
     
  5. gas4you

    gas4you

    Joined:
    23 Feb 2007
    Messages:
    21,178
    Thanks Received:
    1,912
    Location:
    Norfolk
    Country:
    United Kingdom
    Most appliances will state what gas they will use at maximum in m3/hr.

    Add all these figures up then see what meter will comfortably handle this ;)
     
  6. ChrisR

    ChrisR

    Joined:
    24 Jul 2003
    Messages:
    24,298
    Thanks Received:
    1,406
    Location:
    London
    Country:
    United Kingdom
    A U6 = 6 cubic metres an hour will supply 60kW, or a bit over, but the "droop" in the meter can be significant.
    So a U16 could cover it, but they'll only fit one for you for a mere few hundred quid if their supply to it is adequate, If not, they increase the size of their supply - at your expense, which is a lot.


    OOps, I saw the 135, not the 185!
     
  7. clf-gas

    clf-gas

    Joined:
    2 Mar 2007
    Messages:
    3,441
    Thanks Received:
    64
    Location:
    Lancashire
    Country:
    United Kingdom
    Somebody needs to get the Betnovate ready as an aris slapping is on its way :LOL: :LOL:

    ;)
     
  8. doitall

    doitall

    Joined:
    8 Jan 2005
    Messages:
    19,003
    Thanks Received:
    1,538
    Location:
    Bath
    Country:
    United Kingdom
    Cough, Cough.

    185 Kw = 17.29m³h

    An U 16 is 16 m³h close but not quite close enough.
     
  9. clf-gas

    clf-gas

    Joined:
    2 Mar 2007
    Messages:
    3,441
    Thanks Received:
    64
    Location:
    Lancashire
    Country:
    United Kingdom
    Cough, Cough.

    185 Kw = 17.29m³h

    An U 16 is 16 m³h close but not quite close enough

    :LOL: :LOL: :LOL:

    You was warned. now wheres that aris cream :LOL: :LOL:

    ;)
     
  10. Sponsored Links
  11. Biggles..

    Biggles..

    Joined:
    19 Feb 2006
    Messages:
    30,121
    Thanks Received:
    9,208
    Country:
    United Kingdom
    Allowing for diversity factors a U16 might cut the mustard.
     
  12. clf-gas

    clf-gas

    Joined:
    2 Mar 2007
    Messages:
    3,441
    Thanks Received:
    64
    Location:
    Lancashire
    Country:
    United Kingdom
    Steady now Lee, steady, (snigger emoticon)

    ;)
     
  13. GforceJames

    GforceJames

    Joined:
    6 Sep 2007
    Messages:
    335
    Thanks Received:
    7
    Location:
    Essex
    Country:
    United Kingdom
    My fault didn't read the 185kw bit, just saw the 135kw.

    Brain didnt register the rest. Seen similar though on u16 and seem ok, doesn't make it right though.

    James
     
  14. doitall

    doitall

    Joined:
    8 Jan 2005
    Messages:
    19,003
    Thanks Received:
    1,538
    Location:
    Bath
    Country:
    United Kingdom
    Diversity in a Commercial kitchen :eek:

    Good practice would allow at least 10-15% higher than the calculated load.
     
  15. clf-gas

    clf-gas

    Joined:
    2 Mar 2007
    Messages:
    3,441
    Thanks Received:
    64
    Location:
    Lancashire
    Country:
    United Kingdom
    For sure you get diversity in a com kitchen, I meet all nationalities on a daily basis DIA.

    Oh and U25 is the way. on a domestic job now where we have had to upgrade to a U16, two boilers, large range cooker and two fires:cool: , Anyone got a meter tail for 15mm :LOL: :LOL: .

    ;)
     
  16. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,020
    Thanks Received:
    4,591
    Location:
    London
    Country:
    United Kingdom
    Stuart, we know from your past postings ( which have not always been very polite to us who give you advice ) that you are apparently employed to design gas and heating systems.

    Its very galling to a professional that you are able to do that work without having any qualifications or practical experience just because you dont touch actual gas fittings yourself.

    Yet again my advice would be that you need to take sufficient training to be able to do your work without having to ask such basic advice on a free forum.

    Alternatively employ a proper consultant to assist you.

    Can I suggest that qualified people on this forum DONT give him this valuable free advice that he should really know himself or might at least pay for within the project costings.

    Tony
     
  17. sturharv

    sturharv

    Joined:
    4 Sep 2007
    Messages:
    219
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    Ahh Tony, thought you may crawl out of your hole at some point!!

    Again you seem better at slating the actual post rather than putting together a constructive or helpful answer to the actual question. I am not responsible for sizing the gas meters or other items which requires specialist knowledge (although for some reason you seem to know what exactly I do), I am simply curious as how these things work so I can understand what needs to be done i.e. costs for the work etc. so get off your high horse.