Given it's a kitchen/workspace area and you don't need peace and quiet, how about considering forced air heating from the CHW?Cheers Madrab - can you expand on vertical/column rads and why they don't tend to heat up as quickly as conventional rads?
I've taken into account the 22 > 15 > 8mm exisiting pipework and as you say I don't want to upset the system, however there is not alot else I can do to get around this? Can I not just rebalance on the new pipework and rads being added to the system?
Extension area is 8*3m 24m2 it's knocked into existing kitchen that is 3x3 with a small radiator that I could expand on. Therefore instead of adding two new radiators, I could add a large one as the pipework is already run and then modify the existing radiator into a larger one.
According to BTU calcs I'd need around 8000 to heat the 24m2 area space.
I'm here for everyone's experience as I want to obviously take the best approach.
Myson do a range of kickspace or blower units.
Would solve most of your issue here no?