As you have confirmed the IR does rise when a voltage is applied from the Megger and it more than meets the regulations, then I would leave it in, power it up and hope. You could maybe do a retest further down the line, to see if the IR has settled or improved.
I here you, not sure how building inspection will like the Cert with them figures on.