As for the example you go on to give, it's nothing to do with bonding, let alone MEB. The whole point of the design of the various circuits in the house (and the adequacy of their live conductors, CPCs and EFLI) is to ensure that protective devices will operate rapidly (before damage to any cables/CPCs occurs) whenever the potential of exposed conductive parts (which, in effect, includes metal pipework) rises to potentially dangerous levels due to a fault.
So, taking the example I gave - and leave out any bonding/earthing of the pipework.
Which
circuit is not designed properly ?
The RFC is designed properly - if there's a L-E fault in the circuit then the breaker will trip.
The boiler supply is designed properly - if there's a L-E fault in it or the boiler then the breaker will trip and/or the fuse in the FCU/plug will blow.
Connect the live in the larger circuit to the CPC in the other and it's not guaranteed.
Therefore to apply earthing to parts which cannot become live because they are not part of an electrical appliance or accessory is not beneficial.
Some seem to think that live conductors can suddenly jump out and attack random pipes - we do not have to cater for this.
Now we take a hypothetical installation where the sparky has been round and done his bit. And the sparky determined that the water pipes didn't need any earth or bonding connection. What's more, none of his cables are on/close to any pipes.
Then the plumber comes round and puts the plumbing in, and like many plumbers, doesn't seem to care about cables. So somewhere there's a cable sat on a hot pipe. Over time, with the heat and movement, the insulation slowly wears through until fate decided that the live conductor which happened to be on (the wrong side) contacts the pipe.
Because someone didn't cater for it, we now have live pipework with only the boiler wiring to "earth" it - hence an inadequate fault current to make the breaker trip in a timely manner.
But it's alright if anyone dies in the ensuing fire, because it wasn't the sparkies responsibility to account for that - or that's how I read your statement.
Of course, these days the circuit will
almost certainly have RCD protection. That's not the case in older properties that haven't yet been upgraded.
But I believe the regs disagree with you. Bonding of conductive parts in a bathroom
IS required unless certain conditions are met. That sounds very very much to me like those who wrote the regs consider that the electrician
MUST cater for the potential of a live conductor
randomly attacking a pipe.