I had a look at the article which says "the conductor should be continuous"These can either be run separately or via one unbroken cable linking both to the MET.
(this suggests guidance - if there is a regulation it would say "must")
This question has cropped up before - can you find a regulation that says it must be a single unbroken cable?
No, it does not.What the main bonding is doing is 'intercepting' an external earth potential that may be introduced into the building via a gas or water pipe..
It prevents metal parts from becoming live under fault conditions.
Hi bengasman, much appreciated advice. If I didn,t have a cut out hatch, under Fitted carpet, there would be NO other convenient point, other than within the garage, where the boiler/CB/and all pipes are together.That would be ideal for me, except for the 600mm rule.If I covered the floor with other type of flooring, under floor access, would be very difficult, without ripping floor up.This is what makes me think the bonding wasn,t done in the first place.The householder before me, who was/and still is a sparky, intended to bond at garage, 15 metres from gas meter.All the pipes are underfloor.and depth of underfloor access reduces from 3 feet at meter,to 6 inches at garage where all pipework terminates at combi .This was 15 years ago.Any opinion on this would be much appreciated.Not trying to cop out of regs, but trying to make my job easier.CheersAll screwed electrical connections must be accessible for inspection. Whatever way is easiest for you, is the way to go....AS I have to bond within 600mm of gas meter, then run the 10mm2 cable approx 15 metres to the MET, just measured it, under the floor, which is accessable, scrawling,the actual bonding clip is not visible to whoever wants to check it...
If you don't want to connect outside, you can connect inside as close to the meter as is reasonably possible, even if that is more than 600 mm from the meter.
Bear in mind that the inspector will have to put his tester on the clip, so best not to go overboard with the location. Also, the connection must be very clean as the total impedance of the whole meb must be less than 0.05 Ohm.
Hi bengasman, much appreciated advice. If I didn,t have a cut out hatch, under Fitted carpet, there would be NO other convenient point, other than within the garage, where the boiler/CB/and all pipes are together.That would be ideal for me, except for the 600mm rule.If I covered the floor with other type of flooring, under floor access, would be very difficult, without ripping floor up.
Hi Tony, If I don,t clamp within the meter box, and bring cable 15 metres underfloor to garage, which are opposite ends of bungalow,to consumerboard, nobody can test it,or even locate it unless they take carpet up and scrawl undefloor like me.This was the start of the problem. Homeserve couldn,t locate clamp in box, presumed it was elsewhere, I had no idea,at the time, and then they gave me boiler warning cert.That,s when I found it wasn,t bonded at all.Hi bengasman, much appreciated advice. If I didn,t have a cut out hatch, under Fitted carpet, there would be NO other convenient point, other than within the garage, where the boiler/CB/and all pipes are together.That would be ideal for me, except for the 600mm rule.If I covered the floor with other type of flooring, under floor access, would be very difficult, without ripping floor up.
I have not understood why you are unable to put the earthing clamp within the meter box or housing where ever it is fitted?
Tony
DONE.Gone from meter, inside box , to water riser, 600mm, then back to MET.20 metre run.cheers all for advice.Hi Tony, If I don,t clamp within the meter box, and bring cable 15 metres underfloor to garage, which are opposite ends of bungalow,to consumerboard, nobody can test it,or even locate it unless they take carpet up and scrawl undefloor like me.This was the start of the problem. Homeserve couldn,t locate clamp in box, presumed it was elsewhere, I had no idea,at the time, and then they gave me boiler warning cert.That,s when I found it wasn,t bonded at all.Hi bengasman, much appreciated advice. If I didn,t have a cut out hatch, under Fitted carpet, there would be NO other convenient point, other than within the garage, where the boiler/CB/and all pipes are together.That would be ideal for me, except for the 600mm rule.If I covered the floor with other type of flooring, under floor access, would be very difficult, without ripping floor up.
I have not understood why you are unable to put the earthing clamp within the meter box or housing where ever it is fitted?
Tony
You should really start anew thread.Could someone please explain the requirement for a house split into 4 apartments on different levels with each one having its own gas heating and consequently each having its own meter.
Surely the incoming gas pipe should be bonded within 600 mm of entering the building and that should be enough?
Alternatively would it be advisable to bond from inlet pipework to outlet pipework of each individual meter?
I meant “definitely bond” . The bond is from the distribution board to the gas pipe . The gas end is connected within 600mm of the meter outlet or as the pipe (after the meter) enters the property, if the meter is outside. In this context “property” is tge individual dwelling. The connection must be before any branch on the internal pipework.Thanks and sorry! I thought it might be a follow up to others on similar topic.
As far as I am aware there is no primary meter and the tenants on each floor have their own meters so guess this makes them primary.
Could you please explain "defo bond" and if this requires bonding on each meter outlet, where must the other end go?