Hi, Does anyone know the legal requirements regarding the bonding of the mains gas pipe from the meter to the boiler? Does it have to be within a certain distance from the meter, or anywhere along its length, in my case approx 40 feet.
Hi, Does anyone know the legal requirements regarding the bonding of the mains gas pipe from the meter to the boiler? Does it have to be within a certain distance from the meter, or anywhere along its length, in my case approx 40 feet.
Hi Tony, just had Homeserve do a inspection on boiler, couldn,t see bonding on gas pipe at meter, written warning.I thought it was inside of wall, underfloor, aesy to get to.However, none at all.I also cannot see any on water pipes, which come in as lead.Does water need bonding if it,s lead underground? Can I bond gas 600ml from meter to water pipe income, just about 7 metres apart? cheers.If its an external meter and some way from, for example an upstairs flat fed externally, its accepted that the earth bond can be where the gas pipe comes into the flat but still be left visible or inspectable.
In fact Nat Grid seem to recommend that position although its not based on any gas rules or legislation. Sound advice in many cases though.
Tony
Both gas and water must be bonded to the main earthing terminal (MET) of the installation using 10mm2 cable. These can either be run separately or via one unbroken cable linking both to the MET. See this article for more information: http://electrical.theiet.org/wiring-matters/22/bonding.cfm?type=pdf[/QUOTE]Hi, Thanks for the link. As both water/gas both come in approx 40 feet from boiler/ and consumer board, a continuous conductor from gas 600ml from meter, to water, which is all copper, apart from 3 feet of lead input,then to MET seems best choice. Does that sound ok? ps. Does C/H need bonding as well, Circs?
Hi, Thanks for the link. As both water/gas both come in approx 40 feet from boiler/ and consumer board, a continuous conductor from gas 600ml from meter, to water, which is all copper, apart from 3 feet of lead input,then to MET seems best choice. Does that sound ok? ps. Does C/H need bonding as well, Circs?
Thanks Mikely, and Tony.Much Appreciated. It,s only taken Homeserve 7 years to notice this, + other stuff, Boilers 17 years .old, all I want them to do is change C/h Diaphragm.Found 5 piddling faults,+ bonding. and 2 hours later left, no diaphragm change, another day.Already waited a week.Under contract.Good innit:.Think they are trying to tell me something:Hi, Thanks for the link. As both water/gas both come in approx 40 feet from boiler/ and consumer board, a continuous conductor from gas 600ml from meter, to water, which is all copper, apart from 3 feet of lead input,then to MET seems best choice. Does that sound ok? ps. Does C/H need bonding as well, Circs?
Yes, that sounds OK. There is no requirement to separately bond other parts of the C/H, such as the boiler. It is only services that could introduce a voltage (usually earth) into the installation that require bonding to the MET.
As both water/gas both come in approx 40 feet from boiler/ and consumer board, a continuous conductor from gas 600ml from meter, to water, which is all copper, apart from 3 feet of lead input,then to MET seems best choice. Does that sound ok? ps.
Hi Tony, it is as you say. I would have thought lead, being not a bad conductor, coming direct onto copper throughout, would not have needed bonding.But, There,s nothing in the link regarding lead.being a earth pole.There is a old remnant of a bond clip on the lead, long abandoned.They must deem lead not so good a conductor. I,m no sparky.As both water/gas both come in approx 40 feet from boiler/ and consumer board, a continuous conductor from gas 600ml from meter, to water, which is all copper, apart from 3 feet of lead input,then to MET seems best choice. Does that sound ok? ps.
Thats ambiguous!
The 10mm2 earth conductor can go from gas to water and then to meter.
But you cannot rely on the water pipe as the conductor! It has to be 10 mm2 all the way from gas to meter but it can earth other things on the way.
Tony
Hi Mikely, can you clarify for me why the bonding has to be within 600mm of gas meter and water inlet, yet all of the pipes terminate in my garage at the boiler 5 feet from MET.on the same wall.? Whats the reason for running 2 X 40 feet of bonding cable paralell to pipework to MET, when it all can be bonded at 1 point in garage and run 5 feet to MET.Appreciate your advice, it,s very helpful. CheersThe more conductive the water pipe is, the more important it is that it is bonded. The danger presented by gas and water supplies is that they can introduce an earth potential to the building that is different to the earth potential of the electrical supply (at the MET). The main bonding minimises the potential difference between exposed and extraneous conductive parts in the installation during an earth fault.
Tony, you are right that main bonding of an incoming service is not required where the service pipe and pipework within the installation are both of plastic. However, quoting from the BS7671:2008 On-site guide: ‘Where there is a plastic incoming service and a metal installation within the premises, main bonding is recommended unless it has been confirmed that any metal pipework within the building is not introducing earth potential.
Hi Mikely, can you clarify for me why the bonding has to be within 600mm of gas meter and water inlet, yet all of the pipes terminate in my garage at the boiler 5 feet from MET.on the same wall.? Whats the reason for running 2 X 40 feet of bonding cable paralell to pipework to MET, when it all can be bonded at 1 point in garage and run 5 feet to MET.Appreciate your advice, it,s very helpful. CheersThe more conductive the water pipe is, the more important it is that it is bonded. The danger presented by gas and water supplies is that they can introduce an earth potential to the building that is different to the earth potential of the electrical supply (at the MET). The main bonding minimises the potential difference between exposed and extraneous conductive parts in the installation during an earth fault.
Tony, you are right that main bonding of an incoming service is not required where the service pipe and pipework within the installation are both of plastic. However, quoting from the BS7671:2008 On-site guide: ‘Where there is a plastic incoming service and a metal installation within the premises, main bonding is recommended unless it has been confirmed that any metal pipework within the building is not introducing earth potential.