A builder has asked me to look at a kitchen refurb he is doing at a church. In the new kitchen there will be a 6KW water heater for the sink, a 6KW tea making machine, 3 x 3KW plinth heaters, and a 6KW water boiler/cofee machine. Along with the usual lighting and sockets there is a 4.7Kw commercial dishwasher.
The existing supply is 100A 3phase CU.
There is another existing small kitchen with an electric cooker/hob, and a 2KW water heater.
Elsewhere i nthe church there are ring final circuits for sockets and obviouly a fair amount of lighting circuits.
My question is around whether the existing supply is adequate for the additional load as there is no diversity allowed for the water heaters, they alone would add up to 20KW = 86A.
There are 3 spare circuits in the existing board, I was prosing to supply three sub boards from 40A breakers (one on each phase)and spread the load over them.
So in summary, is the supply adequate, and do you agree with the design ?