Discussion in 'Electrics UK' started by Matt_85, 7 Jul 2020.

  1. Matt_85

    Matt_85

    Joined:
    2 Sep 2019
    Messages:
    27
    Thanks Received:
    1
    Country:
    United Kingdom
    Might be a daft question but thought I'd ask regardless.

    We had power (from light circuit) supplied to 600mm above our sinks in our new build incase we wanted a mirror cabinet either on moving in or in the future.

    We've decided we dont want one yet so are simply going to fit a flat mirror above the sinks (adhesive to wall).

    The power supply points are covered with a single gang blank plate.

    When it comes to removing this blank and fitting the mirror, does it need to be done and/or checked by a sparky to ensure compliance or since it's being covered, am I ok to isolate the bathroom/light ring, check it's dead and fit the mirror ? (With silicone around the cut in the tile to prevent water ingress if any)
     
  2. Sponsored Links
  3. DetlefSchmitz

    DetlefSchmitz

    Joined:
    17 Aug 2010
    Messages:
    2,224
    Thanks Received:
    292
    Country:
    United Kingdom
    Leave the plate and space the mirror off the wall. It will look better and do less damage to the wall.
     
  4. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,113
    Thanks Received:
    2,067
    Location:
    Oxfordshire
    Country:
    United Kingdom
    If the plaster is proud of the back box edge, you could chase the blanking plate into the wall so it is flush.
     
  5. Matt_85

    Matt_85

    Joined:
    2 Sep 2019
    Messages:
    27
    Thanks Received:
    1
    Country:
    United Kingdom
    Thanks for the replies

    Detlef, the mirror has no mounting holes and has bevelled edges designed to fit flush to the wall. I could make a box I guess but it could look strange.

    Taylor

    Not sure what you mean. Open the hole in the tile so that the blank plate fits inside and back onto the back box?
     
  6. 333rocky333

    333rocky333

    Joined:
    12 Jan 2008
    Messages:
    8,158
    Thanks Received:
    852
    Location:
    Essex
    Country:
    United Kingdom
    You can get 3mm thick blankplates and as TTC says above you may be able to recess that in flat
     
  7. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,113
    Thanks Received:
    2,067
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Yes, organise it do that the cover plate is recessed. It sounds like you could just remove a tile or two to do this.
     
  8. Matt_85

    Matt_85

    Joined:
    2 Sep 2019
    Messages:
    27
    Thanks Received:
    1
    Country:
    United Kingdom
    Thanks for the reply Taylor, know what you mean now.

    I'll have a look at opening up the hole and flushing the blank plate or putting a thinner one in if it sits proud.

    To Winston's reply (now deleted ?), in this new build after the faults we've had so far, anything is possible lol, inc a lighting ring
     
  9. Sponsored Links
  10. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,113
    Thanks Received:
    2,067
    Location:
    Oxfordshire
    Country:
    United Kingdom
    He may have been moderated.:D :cautious:
     
  11. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    3,997
    Thanks Received:
    803
    Location:
    Durham
    Country:
    United Kingdom
    One slight issue you'll have- if you cover the blanking plate you are removing the safe zone for the cable supplying it. If the cable is floating in a stud wall (or buried more than 50mm behind the surface) then less of an issue, if cable is chased then there's a decent chance you'll forget its there and put a nail through it
     
  12. Matt_85

    Matt_85

    Joined:
    2 Sep 2019
    Messages:
    27
    Thanks Received:
    1
    Country:
    United Kingdom
    Good point.

    The cable is in a stud wall
     
    • Like Like x 1
  13. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,113
    Thanks Received:
    2,067
    Location:
    Oxfordshire
    Country:
    United Kingdom
    If you want to be totally correct, then you need to find where the cable feeds from (in the loft?) and disconnect it there
     
  14. Matt_85

    Matt_85

    Joined:
    2 Sep 2019
    Messages:
    27
    Thanks Received:
    1
    Country:
    United Kingdom
    Each of the three bathrooms has a isolator switch to turn the extractor fan on/off.

    I'm also fairly sure the sparkies said this is fed from the light circuit and that the mirror power points share the power supply with the fan.

    Therefore I presume disconnecting the cable in the isolator would achieve the same result?
     
  15. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,113
    Thanks Received:
    2,067
    Location:
    Oxfordshire
    Country:
    United Kingdom
    The feed probably comes from the lighting circuit. It may be wired from the isolator switch, or it may come from somewhere else. It depends on how it is wired. You’d need to trace the wire (either visually or electrically) to find out.
     
  16. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page