My callout of the day

Joined
26 Mar 2009
Messages
272
Reaction score
21
Location
Wiltshire
Country
United Kingdom
Got called here today, the meter was smoking apparently. Turns out that it they'd had the place re-wired/consumer unit change a few months ago. What was smoking was an ancient ELCB between the meter and the CU. I have serious doubts about the spark who did work here, The main earth is only about 4mm bare, it goes off behind the wall somewhere. the g/y from the new CU is 6mm tri-rated and just the fact that he's left this old ELCB in place when the tails from the meter feeding it were cloth covered VIR of about 8mm! There is an electric shower and allsorts off the CU!
He's chopped off a couple of strands off the new tails to the CU to make them fit in the ELCB terminals and murdered off the screw whilst he was at it. None of the MCB's are labled! And its not fitted straight either!

I re-tailed the cutout and meter and fitted an isolator because the customer had the spark coming later on in the day.

Photo0039.jpg


Photo0038.jpg


Photo0037.jpg
 
Sponsored Links
Sponsored Links

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top