No its a small wall mounted boiler, I dont install Worcesters but went on the course when the 2000 came out, they made a big deal about pumped condensate, it is cear in the Mis , that was a direct quote from the Mis
1. It is a requirement that the condensate drain is installed internally. 2. If external disposal is the only means of condensate discharge, then the CondenseSure siphon or a condensate pump must be installed
Having set up some tubing I can see how the trap inside the boiler can over fill with condensate before it can overcome the back air pressure created by the external trap. An air vent between the two trap solves the problem