Discussion in 'Plumbing and Central Heating' started by David89, 13 Feb 2021.

  1. David89

    David89

    Joined:
    13 Feb 2021
    Messages:
    23
    Thanks Received:
    0
    Country:
    United Kingdom
    My Dad has a fairly old Ecoflam Minor 1 Burner around 20 years old. Serviced last October
    New pump fitted and set up, all cleaned and adjusted and running fine.
    Just before Christmas he called to say the heating had not come on so i popped round and found it locked out. Checked oil (Half Tank) oil reaching pump, bled ok (No Air lock)
    Pushed the re start and it fired straight away and ran perfect again.
    since Christmas this has happened again a few times but always ONLY after a timed start.
    If we leave the heating on continuous, it works fine. Cutting in and out as the temp reaches the set thermostat settings.
    I have then set his next timed event (ie switch on 6am )the next morning, the heating pump comes on but the burner does not fire up. If i then push the Red button, it cycles through pre ignition but NEVER starts on the first push. I wait for 45 seconds and try again, it cycles through and after a few seconds, the solenoid clicks and it starts and runs perfectly until the timed session finishes. It Always starts second push, never on the first ....
    Any ideas would be appreciated.
    TIA
     
    Last edited: 13 Feb 2021
  2. Sponsored Links
  3. snb

    snb

    Joined:
    10 Oct 2007
    Messages:
    3,190
    Thanks Received:
    925
    Location:
    Norfolk
    Country:
    United Kingdom
    most likely the motor coil needs replacing. you can test using a multimeter. probably got a 4uf coil. if reading is more than 10% below it needs changing
     
  4. David89

    David89

    Joined:
    13 Feb 2021
    Messages:
    23
    Thanks Received:
    0
    Country:
    United Kingdom
    The Fan motor?
    I can get someone round to test that and see if it is the problem.
    Thanks
     
  5. oilhead

    oilhead

    Joined:
    29 Nov 2009
    Messages:
    2,140
    Thanks Received:
    510
    Location:
    Shropshire
    Country:
    United Kingdom
    No, just the capacitor as SNB says. Also at this time of year, a weak mixture can occur as the cold air is heavily charged, and over aired causes flame lift off. A good CO2 in september can be very low in february.
     
  6. David89

    David89

    Joined:
    13 Feb 2021
    Messages:
    23
    Thanks Received:
    0
    Country:
    United Kingdom
    Ah right. Sorry if this is a dumb question but, why does the boiler fire up and run second try Every time. It almost seems as if its a fuel starvation issue that clears once its been tried once ?
    TIA
     
  7. oilhead

    oilhead

    Joined:
    29 Nov 2009
    Messages:
    2,140
    Thanks Received:
    510
    Location:
    Shropshire
    Country:
    United Kingdom
    That's a possibility, but we aren't there so cannot comment totally. If fuel starvation was the problem, then after prolonged running one would expect the symptom to show again. Check your filter certainly. The advice you've been given is based upon experience and your description of the fault. Why not get back your engineer from October? You have already appeared to rule out fuel supply problems.
     
  8. Sponsored Links
  9. David89

    David89

    Joined:
    13 Feb 2021
    Messages:
    23
    Thanks Received:
    0
    Country:
    United Kingdom
    Yes I intend to get him round as soon as he can fit us in. With this extreme cold snap he's been swamped out with work.
    Thanks again for all the advice,.
     
  10. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,775
    Thanks Received:
    1,095
    Country:
    United Kingdom
    Is the boiler a Trianco??
     
  11. David89

    David89

    Joined:
    13 Feb 2021
    Messages:
    23
    Thanks Received:
    0
    Country:
    United Kingdom
    No it's an Ecoflam Minor 1
     
  12. oilhead

    oilhead

    Joined:
    29 Nov 2009
    Messages:
    2,140
    Thanks Received:
    510
    Location:
    Shropshire
    Country:
    United Kingdom
    No, that is the make of burner. It will be fitted to a boiler, which could be a Trianco. If so, depending on the model, that may have a bearing on your problem.
    If the boiler does not start from cold, but runs all day, then there may be problem with fuel fall back overnight, but if there is a lazy capacitor, then if you tried once, you have put some charge into the capacitor, then topped it up with the second try. Likewise, if the burner is overaired, the first try will have sprayed some oil into the combustion chamber and round the blast tube, and this with the second dose, richens up the mixture.
     
  13. David89

    David89

    Joined:
    13 Feb 2021
    Messages:
    23
    Thanks Received:
    0
    Country:
    United Kingdom
    OK thanks. I will try to find out the boiler make. I think the only marking on the front is Heat World. Can't find any other markings, sorry.
     
  14. oilhead

    oilhead

    Joined:
    29 Nov 2009
    Messages:
    2,140
    Thanks Received:
    510
    Location:
    Shropshire
    Country:
    United Kingdom
    Heating World is the make. No big problems with them as long as serviced and cleaned out regularly.
     
  15. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page