That is of course accepting that two measurements ( Ze & R1+R2 ) added together is a calculation.
Yes agreed , at best it is part measurement and part calculation usually and an approximation at best. but often good enough within some constrasintThat is of course accepting that two measurements ( Ze & R1+R2 ) added together is a calculation.
... and, as I've said, that is (in my opinion) how one should do it (if one doesn't actually measure Zs with bonding disconnected), since that then gives a 'worst case' answer (i.e. indicating what the Zs would be if parallel paths were to disappear.Yes, that is why Ebee said Zs is calculated by adding Ze to R1+R2 - so that any bonding is discounted.
I took him to mean '... and any rearrangement of that equation', which would therefore include Zs = Ze + (R1+R2) - but you are suggesting that he actually advocated that (despite it being simply a rearrangement of an equation which he said is something that he said we would "never ever ever" use?We never ever ever calculate Zs - Ze = R1 + R2 in Electrics, it is a false equation and so must never be used.
Well, in a literal sense I suppose that adding two things together is 'a calculation', albeit a very trivial one.That is of course accepting that two measurements ( Ze & R1+R2 ) added together is a calculation.
In terms of what the Zs would be if parallel paths to earth were to disappear, adding Ze and (R1+R2) gives an exact, not approximate, answer.Firstly if we know Ze and R1 & R2 then we can surmise Zs approximately therefore the equation holds good ...
Unless one or more of one's measurement/determinations is incorrect, 'measured Zs' (with bonding present) cannot be higher than Ze + (R1+R2). In the presence of bonded extraneous-c-ps, it will be lower - but, as I keepo saying, it would be 'dangerous' to assume that thjose parallel oaths would always exist. As you go on to say ....... and we can measure Zs to see if it confirms it is "in the parish" of what we expect - without bonds.
... but that (calculating Ze from Zs and R1+R2) is not what we're talking about. As you say, Zs measured with bonding in place will commonly be 'optimistic' (which I call potentially dangerous') because it relies on bonded parallel paths remaining present.It is common on say small minor works to just measure the Zs with bonds etc attached and for that reason any Zs we actually measure might be quite optimistic so it is not relevant to deduct Ze to give R 1 + R2 or instead to deduct R1 and R2 to give Ze, it would be too unreliable
Do you mean what you implied by what you wrote in post #60 - namely that Zs should be determined by adding Ze to R1+R2 ("to discount bonding"), and not by direct measurement (with bonding present)?I might have got confused by who said what and all the formulae. Just take what I wrote as the way I think it should be done.
It's not such a problem in my house, because it is 'declared' and treated (by me) as TT, so people would presumably not be expecting the Zs of any circuit to be low enough for OPD-mediated ADS (and would, instead, look for the RCD protection).As in your house, you cannot count the water pipe as part of the Ze or Zs in case it disappears one day.
Yes, I mean that.Do you mean what you implied by what you wrote in post #60 - namely that Zs should be determined by adding Ze to R1+R2 ("to discount bonding"), and not by direct measurement (with bonding present)?
Ok.If so, that's essentially what GN3 seems to be saying firts mentioning tyhe 'calculation' (from Ze and R1+R2),
A measurement, from the farthest point of the circuit, lower than [Ze + R1+R2] will show that the circuit is connected correctly and actually has a Zs measurement.before mentioning "by direct measurement" (with bonding present) - and then goes on to say that one should 'take into account' (as, I've asked, "how?") the fact that such a figure will, in some senses, be 'erroneous' (in a 'potentially dangerous' direction) if there are any bonded extraneous-c-ps.
Yes, I know - as it should be.It's not such a problem in my house, because it is 'declared' and treated (by me) as TT, so people would presumably not be expecting the Zs of any circuit to be low enough for OPD-mediated ADS (and would, instead, look for the RCD protection).
Hence why it should be done as I am saying.As I've said, the 'real potential danger' of Zs measurements with bonding connected is in TN installations - since those measurement may 'confirm' that Zs figures are low enough to achieve the required disconnection times with the bonded metal water pipe present, but Zs might become too high to achieve those required disconnection times if (as can certainly happy=en) the metal pipe were to "disappear one day". As I've said,that would sound like a "C2" to me - to be acceptable, I think I would want to see a Zs measured with bonding disconnected, to conform that disconnection times would still be achieved even if the metal pipe were to disappear.
OK - so you, myself and (partially) GN3 say that's how it should be done, but GN3 also says that Zs may be determined "by direct measurent" (with bonding connected) and I strongly suspect that such is what many people do (plug in their MFT and press the button") - in which case, as I keep saying, the result can be misleadingYes, I mean that. Sorry, I must have misread The thread.
Yes, it shows that - but, as I said, if it's done with bonding connected, it can give a misleading answer, because and apparently 'low enough' Zs (to achieve required disconnection times) might cease to be 'low enough' if the bonded extraneous-c-pwere to disa[ppear.A measurement, from the farthest point of the circuit, lower than [Ze + R1+R2] will show that the circuit is connected correctly and actually has a Zs measurement.
As above, we seem to be agreed about that, BUT it remains my suspicion that ('supported by GN3") many people probably just 'measure Zs' (with bonding connected).Hence why it should be done as I am saying.
Absolutely John, that was what I was trying to imply. Although we might accept a Zs knowing that in some cases that Zs is potentially optimistic we must not use it in the equation in order to calculate back. Too risky.As you say, Zs measured with bonding in place will commonly be 'optimistic' (which I call potentially dangerous') because it relies on bonded parallel paths remaining present.
Yes, exactly, so is only allowed on minor works like additions etc, any proper work, (rewire, CU change) then no, the bonds etc must be removed (even with all the potential danger it brings in, which must be mitigated)OK - so you, myself and (partially) GN3 say that's how it should be done, but GN3 also says that Zs may be determined "by direct measurent" (with bonding connected) and I strongly suspect that such is what many people do (plug in their MFT and press the button") - in which case, as I keep saying, the result can be misleading
I don't really understand your position since you, EFLI and myself seem agreed that it is not 'safe' to rely on a direct measurement of Zs with bonding connected - so that (if Zs is to be measured with bonding connected) the only 'safe' way to determine Zs is by using 'the equation' [based on (R1+R2) and a measurement of Ze without bonding ] - but you seem to be suggesting the opposite in the above.Absolutely John, that was what I was trying to imply. Although we might accept a Zs knowing that in some cases that Zs is potentially optimistic we must not use it in the equation in order to calculate back. Too risky.
See above. If Zs is going to be measured with bonding connected, it seems that the only 'safe' way of determining Zs (the Zs that there would be if parallel paths were to disappear) is by using the equation?As a pure maths exercise yes you can do that but as equation for electricians to use the NO. Dont do it, tends to get hammered into us at college etc and quite rightly.
I on't really understand what you mean by 'back calculation' - if one arrangement of an equation is acceptable, then so is any other arrangement - as with Ohm's law (i.e. given any two of current, résistance and voltage, one can calculate the third).If you want to measure or calculate Ze then fair enough, similarly with R1, R2, Zs, but never use the results as a "back calculation" ...
Can you clarify? As you will understand, I don't really follow your reasoning.far too much change of additional error in that method, there are already more than enough chances of error using our best efforts (meter accuracy, events on the day, ambient temp etc etc)
Needless to say, I agree - but the only 'guidances' I've ever seen say that one should not disconnect bonding when measuring Zs, and I don;t think I've ever seen an electrician do that.Yes, exactly, so is only allowed on minor works like additions etc, any proper work, (rewire, CU change) then no, the bonds etc must be removed (even with all the potential danger it brings in, which must be mitigated)