Prior to 16th Amendment 1 2002, the requirement was for the cable capacity to be 0.67 x In. Has there always been a correction factor for rewirable fuses? When they were all that were ever used (in homes) it seems a bit AAF for you to have needed a correction factor all the time
In the 14th you had
"close protection",
will operate within 4 hours at 1.5 times the designed load current of the circuit.
and
"coarse protection"
will not operate within 4 hours at 1.5 times the designed load current of the circuit
Rewirable fuses were coarse protection
All the tables for cable ratings were for coarse protection
Above each table was-
The tabulated ratings may be multiplied by1.33 if close excess current protection could be assured
A 2.5 T+E enclosed cable in the table was rated at 18 amps for coarse,
so if an mcb was used 18 x1.33 was 23.94 amps