Hello,
I would appreciate your comments on my proposed solution to supplying a stone outbuilding from a portable generator.
I have read the numerous posts on this and other forums, and http://electrical.theiet.org/wiring-matters/39/portable-generators.cfm?type=pdf and distilled it all into the solution below.
The aim is to power the outbuilding (club hut) for an hour or two once a week.
The design criteria are that:
A) power is supplied from one of several peoples' personal portable generators (~3kVA type), taking the generator away each night for security
B) sighting the generator away from the clubhouse for noise reduction,
C) use an easy-to-coil lead running from generator to clubhouse.
D) have one single, simple connection to hook up generator to clubhouse
The outbuilding (stone shed far away from grid electricity) is wired with small consumer unit(CU) with RCD protected ring main and lighting circuit. This Consumer unit is therefore to be fed from a floating neutral portable generator sited some distance away via suitable rubber extension lead.
You will see that there are several issues with the above that I need to address, namely:
a) bond the earth and neutral at the generator, so that CU RCDs can operate from the otherwise floating-neutral generator
b) provide suitable ground rod for fault current path/ground reference for RCD
c) provide protection for the extension cable running from the generator to the CU (it is proposed to be rubber not armoured for ease of coiling)
I would appreciate your comments on my proposed solution:
1) bond earth and neutral inside a 16A 'commando' plug for connection to portable generator. This way the generator remains unaltered for the person to take home and use as normal.
2) connect this commando plug to an inline 16A 30mA RCD (e.g. http://www.toolstation.com/shop/p22113) via a short (10cm) length of SWA (hence this short length needn't have RCD protection)
3) the protected side of this inline RCD is then led to the clubhouse via a 15m rubber-coated 3 conductor extension lead (suitably sized). This way the entire length of the connection from the generator to the clubhouse is protected yet easier to handle than a whole reel of SWA.
4) the ground rod is installed at the outbuilding end and permanently wired to the earth bar of the CU, this way the connection can be made permanent and good, and the generator connected by plugging a single 16A plug into the generator.
My main concern is with the ground rod arrangement.
I would prefer to keep the ground rod permanently installed at the CU, so as to avoid having to make up a good connection from the ground rod to the generator each time the generator is connected (only one plug to connect)
QUESTION 1: Is it sufficient to have the ground rod permanently connected at the C.U. instead of close to the generator?
For the connection inside the clubhouse to the CU, for neatness I would like the extension lead to have plugs/sockets at each end so it can be disconnected and stored away from rodents (i.e. a pair of 16A plug/sockets, one on the wall for the CU, one on the cable)
My concern is that if someone plugs one end of the extension lead into the generator(with its neutral-ground link) yet neglects to plug the other end into the CU (and hence the ground rod), then the generator frame will be at a 'high' neutral potential and a shock risk? A ground rod at the generator end would negate this risk so long as the connection were made sound each time, but I'm trying to avoid this if possible as it relies on the user connecting the ground as well as the main extension cable
QUESTION 2: I assume that all floating-neutral portable generators have their frames connected to the earth pin of the output, and therefore the frame would be suitably grounded via the extension lead to the ground rod at the CU?
many thanks in advance for any observations/advice.