Why is it better without an Earth ? The only reason that it could be "better" is that it avoids the risk of electric shock from an exported Earth that is not a Ground potential.
It is also cheaper to produce a ( so called ) Class 2 device and self certify that is by virtue of it's design Class 2 ( that route avoids the need to actually test it is Class 2 )
Earthing is not a good thing in its own right. It is a necessary evil in order to disconnect the supply in the event of a fault anywhere on the installation which makes live all the exposed metal parts of electrical items.
Removing the need to earth metal parts by double insulation and/or plastic construction is therefore considered better.
It would be better if nothing ever needed earthing.
The only reason that it could be "better" is that it avoids the risk of electric shock from an exported Earth that is not a Ground potential.
Why is it better without an Earth ? The only reason that it could be "better" is that it avoids the risk of electric shock from an exported Earth that is not a Ground potential.
No. As EFLI has said, 'unnecessarily' creating any additional touchable earthed metal (whether or not related to an electrical installation) increases the chance of electric shock, by increasing the possibility that someone would be in contact with 'a second point of contact' (at earth potential) at the same time as they came in contact with something 'live'.
Indeed. If there is a plug fitted to the cable, then that removes any uncertainties as to what is, and what is not, 'fixed wiring'.
In the real situation we are discussing (with no plug on the cable), I still find it odd that, if the connection between CU and an item of Class II equipment consists of two bits of cable, joined at a JB (or equivalent), that whether or not the downstream bit of cable requires a CPC appears to depend on who connected that bit of cable to the item.
Outdoor floodlight with Live and Nuetral fed to it. Double insulated so perfectly safe.
Floodlight overheats and catches fire, not enough fault current to trip the over current protection device, Charged mass with Live and Neutral conductors in insulation that has burnt and been carbonised, carbon is conductve even if the plastic it came from was totally insulating the Live and Neutral before the fire.
Ingress of water is another way the exterior can become Live and again no tripping of a safety disconnect until some one touches the device while also in contact ( direct or indirect ) with Ground and takes enough current through their body to trip the RCD ( if an RCD has been fitted ).
And don't forget the "tingle" or "buzz" that some people feel on the exterior metal of some apploance and laptops which are supplied with ELV ( 19 volts for laptops ) from a double insulated no earth required power supply module. The ELV supply is floating around the mid point of Live and Neutral. ( 115 volts AC ). The ELV is capacitively pulled to the mid point and as such there current in the "tingle" is very small as long as the Power supply is in good condtion and is not damp.
Floodlight overheats and catches fire, not enough fault current to trip the over current protection device, Charged mass with Live and Neutral conductors in insulation that has burnt and been carbonised, carbon is conductve even if the plastic it came from was totally insulating the Live and Neutral before the fire.
I am suggesting that a risk assesment of the various ways an item of electrical equipment can fail should be made and if necessary common sense applied to arrive at a solution.
I am suggesting that a risk assesment of the various ways an item of electrical equipment can fail should be made and if necessary common sense applied to arrive at a solution.
There will be when the Line and Netral insulation melts.
Charged mass with Live and Neutral conductors in insulation that has burnt and been carbonised, carbon is conductve even if the plastic it came from was totally insulating the Live and Neutral before the fire.
Ok. So how do you ensure that the live conductor (or Neutral if there is an RCD) will connect to the CPC when it did not short to the neutral (or Line)?
Ingress of water is another way the exterior can become Live and again no tripping of a safety disconnect until some one touches the device while also in contact ( direct or indirect ) with Ground and takes enough current through their body to trip the RCD ( if an RCD has been fitted ).
Are you forgetting the exterior is plastic (or similar)?
Where exactly do you affix the unnecessary CPC to ensure it is in the live water track or area likely to be carbonized?
What about TTing it as well just to be on the safe side?
"Common sense" It seems it only works one way, doesn't it?
If, indeed, that is what is being used.
I am suggesting that a risk assesment of the various ways an item of electrical equipment can fail should be made and if necessary common sense applied to arrive at a solution.
I am suggesting that a risk assesment of the various ways an item of electrical equipment can fail should be made and if necessary common sense applied to arrive at a solution.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local