DoItAll said:
in the example the 2 Chris's work out, the accumulator would best deliver 12litres a minute.
That isn't true.
I was hoping to hear the bath would fill in 30 seconds!
The flow you're getting is much the same a standard pump of a similar head might provide, with such a low pipework resistance (each side of a twin):
Softus said:
So is the accumulator providing more than four times the mains flow rate? If so, is it correct to infer that the accumulator is providing more than four times the mains pressure?
Yes and no.
If you filled a 200 litre cistern from a mains supply providing just 1litre per minute then tipped it over your head you could experience 200 times the mains flow - but not for long.
The pressure would depend how high the cistern was...
---
If the flow at the bath tap were only 18 litres/minute, the dynamic pressure, at the point in the plumbing where the accumulator is, would be much lower off the mains if the pipework took that route.
Even at 40 l/min (one tap, one pipe, one tank) he's only losing about a bar from the tank to the tap (about 6m in the pipe if it's straight). Say the pressure at the tanks having discharged some water is 2 bar (could work it out but its late). That implies that the resistance of the mains is such that he must be losing of the order of 2 bar between the road and the tank point. (Making 1 bar at the tank point, half the pressure so half the flow... roughly...)
If the main to that point is 15mm equivalent, it would need to be 40 metres equivalent length - perfectly feasible.
[Edit - That was working with 18 l/min through a 15mm pipe. In this house however the H & C both have to be fed by the mains because there's no storage so the pressure drop is over a metre head per metre run in 15mm. If the mains were replaced by 28mm its resistance , and the head lost through it, would go down by a factor of 6, and those measured flow rates again become perfectly achievable.]
You can have any flow rate you like if - as explained in earlier posts - you get the resistance low enough.
So nothing surprising in the figures measured.
The only surprise is what these particular pressure vessels cost, when there are other means of achieving similar or better performance in a smaller space.