This post is the conclusion to date of two gas fitter visits and an element of self help which have both failed to deal with matters satisfactorily.
I have a Potterton Performa 24 which was playing all sorts of tricks and I had the PCB and a couple of microswitches replaced some 3 months ago. Within a couple of days it reverted to one of its previous faults, when the HW was fired it was also feeding the radiators. The gas fitter said the diverter valve itself was fine at the time and the PCB was the issue. Prior to this, I had the diaphragm replaced a year ago by a GS qualified family friend who was fortunately in the area, but it didn't help and he advised me to replace the diverter.
Just this week, the boiler has started cutting out when either HW or CH are operated. Initially the boiler fires for some 2 minutes before cutting out and then fires up again within 10 seconds. It then repeats this cycle albeit at reduced 30 second intervals.
I took the DHW heat exchanger out tonight, cleaned it with domestic descaler and rinsed for a couple of hours before refitting. Unfortunately this did not work. No issues with pressure, a steady 1.5 bar. The heating outflow 22mm pipe on the far left does get hot. No warning lights.
I noticed that the top chamber of the heat exchanger is coated with a black almost carbon like substance, but not blocked. Some of this came out when I cleaned it, but a coating still remained. Is this a red herring or should I do the job again using something like Fernox F3?
Whilst I'm at it I'm tempted to tackle the diverter as well. This is effectively two separate components on the Performa 24. Do I need to replace both? This may even be the root cause of everything?
Any pointers or even alternative suggestions would be gratefully appreciated.
This post is the conclusion to date of two gas fitter visits and an element of self help which have both failed to deal with matters satisfactorily.
I have a Potterton Performa 24 which was playing all sorts of tricks and I had the PCB and a couple of microswitches replaced some 3 months ago. Within a couple of days it reverted to one of its previous faults, when the HW was fired it was also feeding the radiators. The gas fitter said the diverter valve itself was fine at the time and the PCB was the issue. Prior to this, I had the diaphragm replaced a year ago by a GS qualified family friend who was fortunately in the area, but it didn't help and he advised me to replace the diverter.
Just this week, the boiler has started cutting out when either HW or CH are operated. Initially the boiler fires for some 2 minutes before cutting out and then fires up again within 10 seconds. It then repeats this cycle albeit at reduced 30 second intervals.
I took the DHW heat exchanger out tonight, cleaned it with domestic descaler and rinsed for a couple of hours before refitting. Unfortunately this did not work. No issues with pressure, a steady 1.5 bar. The heating outflow 22mm pipe on the far left does get hot. No warning lights.
I noticed that the top chamber of the heat exchanger is coated with a black almost carbon like substance, but not blocked. Some of this came out when I cleaned it, but a coating still remained. Is this a red herring or should I do the job again using something like Fernox F3?
Whilst I'm at it I'm tempted to tackle the diverter as well. This is effectively two separate components on the Performa 24. Do I need to replace both? This may even be the root cause of everything?
Any pointers or even alternative suggestions would be gratefully appreciated.