I had a very strange condition this week, all power to house failed. I turned off all MCBs except one lighting circuit - one CFL then illuminated. Mains input was 138v, and it dropped further as load was added.
Called DNO, 2 truly brilliant guys from SP came out, and diagnosed within minutes that the fault would be broken joint where my service cable meets the main across the road. Correct of course. At least my problem must have been in the Line conductor. If it had been the Neutral/Earth, the effect on my PME would have been nasty.
Supply back on by bedtime, really excellent service. The fault appears to be very common, not good for cable <20 years old. I wonder if it is that common in all areas now?
Called DNO, 2 truly brilliant guys from SP came out, and diagnosed within minutes that the fault would be broken joint where my service cable meets the main across the road. Correct of course. At least my problem must have been in the Line conductor. If it had been the Neutral/Earth, the effect on my PME would have been nasty.