Pressure loss problem with Ferroli F30 combi-boiler

Discussion in 'Plumbing and Central Heating' started by gingerboyblue, 11 Nov 2010.

  1. gingerboyblue

    gingerboyblue

    Joined:
    11 Nov 2010
    Messages:
    1
    Thanks Received:
    0
    Location:
    West Midlands
    Country:
    United Kingdom
    Hi, can anyone help please?
    I have gone through most of the posts regarding pressure loss, but I am still struggling to solve the problem. I shall try and be as comprehensive as I can in explaining what the problem is and what I have done so far:

    Model: (2002 Ferroli F30)
    Problem:
    I am having to top up the CH system pretty much every morning as the pressure drops to 0.5 Bar, causing the boiler to trip out and not supply CH and/or hot water.
    I have thoroughly checked for leaks and there are definately none apparent anywhere in the system.
    There is no water coming out of the air valve in the expansion vessel, but I did have to top up the charge as it was low (did this with a foot pump and charged the expansion vessel to 1.0 Bar). This has increased the amount of time between having to top up the system, but not solved the problem.
    I have bled the system to ensure that there are no air locks.
    When the boiler is running for CH, the pressure continues to rise until it reaches 3.0 Bar and the pressure relief valve operates. When the boiler cools during the night (when CH is off) this is obviously causing the pressure loss due to the contraction of the water/expansion vessel - resulting in the boiler tripping out.
    Here's the weird bit; everytime the boiler trips out, there is only what I can describe as the sound of high pressure air passing through a valve and this happens at around he same time every day (approx 06:30am) although this may just be a coincidence with the temperature drop.

    Am I looking at replacing the expansion vessel or could there be other (more expensive) problems and should I cut my losses and have a new boiler.

    Any help or advice would be very much appreciated.

    Kind regards

    Simon
     
  2. Sponsored Links
  3. kevplumb

    kevplumb

    Joined:
    18 May 2004
    Messages:
    23,711
    Thanks Received:
    925
    Location:
    depends where i get sent
    Country:
    United Kingdom
    check the prv pipe outside :idea:

    if you have precharged the expansion vessel to 1 bar with the system drained

    then it sounds as if its to small for the system :idea:
     
  4. ecowarrior

    ecowarrior

    Joined:
    21 May 2010
    Messages:
    10,201
    Thanks Received:
    2,909
    Location:
    Northamptonshire
    Country:
    United Kingdom
    If mem serves me right the F30 has oblong exp vess on RHSide. It has the valve on the bottom (crap idea) they collect water & rust. Lock of flow & rentern valves & drain boiler via PRV. Go to halfords spend 50p on a new shrader valve. ( get a removing tool £1.50) Replace the rusty one in the Exp vess recharge (system must b empyy) and hey presto.
     
  5. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom