1st off, that's the wrong gauge, that only goes up to 1 bar on a 3 bar PRV.
That could be a verifiable check valve and the plastic cap is the verifiable section. It could also be an outlet for a gauge for a gauge. Hard to say, take it off and see what's underneath?
That PRV has been made up though, with different sections added. The check valve looks like it has been added as well as the male nipple outlet.
OK - TBH a 3 bar PRV wouldn't normally be used as part of a loop for a sealed system. Anytime a PRV would be used as part of a boiler setup would be say to protect a combi and ensure the cold mains inlet didn't exceed 3 bar.
A (R24) filling loop needs an isolating double check valve on the cold mains side, an isolation valve on the system side and a braided hose to connect. If you are looking to have the loop provide a system pressure gauge then you do get filling loops with integrated gauges.
There should really be a valve on both ends of a filling loop to allow it to be fully isolated.
You get 2 kinds of double check valves, verifiable and non verifiable - one would usually have a screw that can be removed to see if the valve is passing, the other doesn't, I've never seen a check valve like that that will take a gauge.
If you look at my pic, the one at the top has the screw, that's the verifiable double check valve, the one on the bottom is just a valve with a body section that the gauge screws into. If the valve on the right of your pic is a check valve then I wouldn't think that plastic cover would be for a gauge as it would be in the middle of the check valve but again if you take it off and have a look.
This is what has been bought on ebay store. I am trying to put it to seal my system from OV.
I have attached a Robofil Auto fill loop from internet. Picture on the left is the actual photo that I bought.
Not normally what would be used for a filling loop. As suggested, no need for the PRV. Only thing that is missing really is the double check valve with an isolator unless a gauge is needed then the pic I attached is really the normal setup.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local